APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:17 AM . Last Modified: 2024-03-12 04:35 AM
Hi all
Please more detail explain
A. Load Display shows the power being drawn by the load so you can avoid exceeding capacity.
B. On-line LED. lights when the UPS is drawing utility power and performing double conversion to supply clean power
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:17 AM . Last Modified: 2024-03-12 07:48 AM
Assuming you're talking about this front panel or similar (if not, please specify)
Load display is the bar graph on the left hand side with the image of a computer below it. This lights up accordingly to give the user a visual representation of the current load percentage on the UPS. Thus, the user knows if all of the LEDs are lit, the UPS load is very high and should be reduced. If no LEDs are lit, the load is very low. As outlined in the UPS user's guide, each LED represents a particular load percentage. i.e. one LED lit may represent ~15% of load. The user's guide should note this.
Online LED - this indicates the UPS is operating off of mains/utility power. You reference "double conversion" so I assume you're looking at a Smart UPS RT or similar. This means the UPS is not operating on battery power input power but if input power is lost, the UPS would go to battery power.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:17 AM . Last Modified: 2024-03-12 07:48 AM
Assuming you're talking about this front panel or similar (if not, please specify)
Load display is the bar graph on the left hand side with the image of a computer below it. This lights up accordingly to give the user a visual representation of the current load percentage on the UPS. Thus, the user knows if all of the LEDs are lit, the UPS load is very high and should be reduced. If no LEDs are lit, the load is very low. As outlined in the UPS user's guide, each LED represents a particular load percentage. i.e. one LED lit may represent ~15% of load. The user's guide should note this.
Online LED - this indicates the UPS is operating off of mains/utility power. You reference "double conversion" so I assume you're looking at a Smart UPS RT or similar. This means the UPS is not operating on battery power input power but if input power is lost, the UPS would go to battery power.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.