APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:16 PM . Last Modified: 2024-03-07 12:29 AM
Hi,
we have just recently replaced batteries in a Smart UPS C 1000i ( SMC1000i )
That is:
Power of the server.
Power off the UPS.
Replaced the batteries.
Power up the UPS.
Power up the server.
But according to Powerchute the new batteries is not detected.
Still the old info available: Aged battery...3,45 years old etc....
Shouldn´t the UPS be "smart" enough to detect the new batteries ?
If not, how do we "tell" the UPS this fact ?
br/Tomasf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:16 PM . Last Modified: 2024-03-07 12:29 AM
pull the batteries while the unit is on, this causes my SMT2200i to ask if they have been replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:16 PM . Last Modified: 2024-03-07 12:29 AM
Fixed !
Thanks Bill !
BR/Tomasf
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.