Hello everybody, I'm new to the forum. I need your help. I bought a used apc 7721 Rack Automatic Transfer Switch and when I press the button to see IP it tells me that IP is 0-0-0-0.
What should I do to change it ????
Thanks to those who can help me.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:29 PM . Last Modified: 2024-02-14 03:19 AM
I tried, the reset works but does not clear IP. Now I buy a serial cable to connect ats to the computer and change IP. Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:29 PM . Last Modified: 2024-01-31 03:01 AM
Hi Franco,
I find the easiest way is to connect the ATS to a network with DHCP and then power cycle the unit. If you need a static address it can then be set in the WebGUI.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:29 PM . Last Modified: 2024-02-14 03:19 AM
Ok thanks a lot, I'll give it a try and I'll let you know.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:29 PM . Last Modified: 2024-02-14 03:19 AM
Hi Gavan, I downloaded the software from the apc official site and I managed to change IP but I made an error. I renamed IP like this: 198.162.0.33. Now I can no longer access it from the browser or from the Apc program. I believe there is an IPV4 problem, but I don't know how to fix it, can you help me ????
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:29 PM . Last Modified: 2024-01-31 03:01 AM
If you hold the reset button for 30 seconds it will reset the ATS to factory default. You can then start again.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:29 PM . Last Modified: 2024-02-14 03:19 AM
I tried, the reset works but does not clear IP. Now I buy a serial cable to connect ats to the computer and change IP. Thank you.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.