Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
HTTPS ERR_SSL_VERSION_OR_CIPHER_MISMATCH
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-0603:58 AM
HTTPS ERR_SSL_VERSION_OR_CIPHER_MISMATCH
Hi,
I was able to successfully to upload SSL certificates to my APCs (AP9631) created with NMCSecurityWizardCLI.exe. However when I try now to access via https I get this error: ERR_SSL_VERSION_OR_CIPHER_MISMATCH
Analyzing the traffic with WireShark I can see handshake failures:
Tried with different browsers and multiple APCs - any idea what could be the problem?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-1110:07 AM. Last Modified: 2021-08-1110:08 AM
Hi Martin,
From the pcap, it looks like the one device is expecting a TLS 1.2 response, and the other is giving a TLS 1.0. You can set the minimum protocol on the NMC to TLS 1.2 under Configuration --> Network --> Web --> Access