Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Float voltage fluctuating but mostly too low
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-2307:44 AM
Float voltage fluctuating but mostly too low
We have some 70+ APC Smart-UPS SMT1000RM2U units deployed at small wireless repeater sites. They are monitored via AP9630 management cards. Typically, the battery voltage reported by SNMP is 27.0 volts which seems correct for floating 24 volts of sealed lead acid cells.
However, we now have several sites where the reported battery voltage is much lower most of the time, going up approximately once every week to 27.0 volts for 24-30 hours and then back down for the rest of the interval. I've attached a SNMP record for the last month at one such site.
We recently had a commercial power outage while the battery voltage was reported as 26.0v and indeed, during the power outage, the battery voltage declined much more rapidly than I would have expected had the batteries been correctly floated at 27.0v.