Hi! How to enable modbus on old SURTD3000XLI? My UPS does not have LCD screen.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:37 AM . Last Modified: 2024-03-18 01:15 AM
Hi Denis,
Modbus is not natively supported on a SURTD model UPS. You would need to purchase a smart-slot accessory, the AP9630/31/35 network management card. The AP9630/31 have support for Modbus TCP (as of firmware rev v6.4), and the AP9635 supports Modbus TCP and RTU (also as of firmware rev v6.4).
Here's the register map for the SURTD: http://www.apc.com/salestools/LFLG-A32FWS/LFLG-A32FWS_R1_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:37 AM . Last Modified: 2024-03-18 01:15 AM
Hi Denis,
Modbus is not natively supported on a SURTD model UPS. You would need to purchase a smart-slot accessory, the AP9630/31/35 network management card. The AP9630/31 have support for Modbus TCP (as of firmware rev v6.4), and the AP9635 supports Modbus TCP and RTU (also as of firmware rev v6.4).
Here's the register map for the SURTD: http://www.apc.com/salestools/LFLG-A32FWS/LFLG-A32FWS_R1_EN.pdf