I hope someone can shed some light on this issue I have!
I have installed 4 new UPS, 2X SMX2000RMLV2UNC and 2X SURT6000RMXLT3U with AP9631 management cards.
I built up the config on the first one and created a config file I used to deploy the others.
Last week, everything was working fine.
We turned them on last weekend, and now, I get continuously kicked out of the management website. It takes less than a minute and I'm out, no error message, nothing.
When I try to log in, I get the message that another user is logged in already. Then I have to go to loginpage/logout.htm to log out and log back in.
I tried with bot IE10 and Chrome, same problem.
And as I am typing this message, the problem seems to have corrected itself and I do not get errors any longer...
Has anyone ever experienced this problem?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
This does not happen all that regularly without some type of cause - I mean one hang up once in a while here and there I may expect but nothing too frequent.
Can you give me the event.txt from the Network Management Card to review please?
Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
I hope someone can shed some light on this issue I have!
I have installed 4 new UPS, 2X SMX2000RMLV2UNC and 2X SURT6000RMXLT3U with AP9631 management cards.
I built up the config on the first one and created a config file I used to deploy the others.
Last week, everything was working fine.
We turned them on last weekend, and now, I get continuously kicked out of the management website. It takes less than a minute and I'm out, no error message, nothing.
When I try to log in, I get the message that another user is logged in already. Then I have to go to loginpage/logout.htm to log out and log back in.
I tried with bot IE10 and Chrome, same problem.
And as I am typing this message, the problem seems to have corrected itself and I do not get errors any longer...
Has anyone ever experienced this problem?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
I validated, I am also on v5.1.7 thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
This does not happen all that regularly without some type of cause - I mean one hang up once in a while here and there I may expect but nothing too frequent.
Can you give me the event.txt from the Network Management Card to review please?
Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
Here is the copy of the log from today and yesterday, I'm MC6
I think I found out what is happening, looks like I have two ip right now on my PC and it's logging from different IPs!
I disabled my wifi link, I'll check out to see if it fixes the issue.
Thanks!
Date | Time | Event | Code | ||
19.02.2014 | 15:32:51 | System: FTP user 'apc' logged in from 10.248.12.76. | 0x0016 | ||
19.02.2014 | 11:38:25 | System: Web user 'mc6' logged out from 10.248.12.76. | 0x001F | ||
19.02.2014 | 11:28:20 | System: Web user 'mc6' logged in from 10.248.12.76. | 0x0015 | ||
19.02.2014 | 10:45:44 | System: Web user 'mc6' logged out from 10.248.12.76. | 0x001F | ||
19.02.2014 | 10:26:24 | System: Web user 'mc6' logged in from 10.248.12.76. | 0x0015 | ||
19.02.2014 | 08:23:11 | System: Web user 'mc6' logged out from 10.248.16.129. | 0x001F | ||
19.02.2014 | 08:11:42 | System: Web user 'mc6' logged in from 10.248.16.129. | 0x0015 | ||
19.02.2014 | 08:07:28 | System: Web user 'mc6' logged out from 10.248.12.76. | 0x001F | ||
19.02.2014 | 07:57:00 | System: Web user 'mc6' logged in from 10.248.12.76. | 0x0015 | ||
18.02.2014 | 16:20:23 | System: Web user 'mc6' logged out from 10.248.16.129. | 0x001F | ||
18.02.2014 | 16:20:17 | System: Configuration change. Email 'from' address. | 0x0033 | ||
18.02.2014 | 16:19:50 | System: Web user 'mc6' logged in from 10.248.16.129. | 0x0015 | ||
18.02.2014 | 14:23:10 | System: Web user 'mc6' logged out from 10.248.12.76. | 0x001F | ||
18.02.2014 | 14:13:01 | System: Web user 'mc6' logged in from 10.248.12.76. | 0x0015 | ||
18.02.2014 | 13:26:59 | System: Web user 'mc6' logged out from 10.248.12.76. | 0x001F | ||
18.02.2014 | 13:26:30 | System: Web user 'mc6' logged in from 10.248.12.76. | 0x0015 | ||
18.02.2014 | 13:20:03 | System: Web user 'mc6' logged out from 10.248.16.129. | 0x001F | ||
18.02.2014 | 13:09:55 | System: Web user 'mc6' logged in from 10.248.16.129. | 0x0015 |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:16 AM . Last Modified: 2024-03-05 01:37 AM
Thank you - and yes, I agree, multiple sessions! Let's monitor and let me know if you think it is related to something else.