Ok, just want to make sure I am not crazy here.
I plugged a serial cable on the back of a Smart-UPS 1400 to use to communicate with some software on a laptop in one of my racks.
When I plug the DB9 serial cable into the port on the UPS, the UPS completely shuts down and turns off.
I have to reset it and turn it back on.
Why would this happen and is this normal?
Thanks,E
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:28 AM . Last Modified: 2024-03-08 12:02 AM
Ok, just want to make sure I am not crazy here.
I plugged a serial cable on the back of a Smart-UPS 1400 to use to communicate with some software on a laptop in one of my racks.
When I plug the DB9 serial cable into the port on the UPS, the UPS completely shuts down and turns off.
I have to reset it and turn it back on.
Why would this happen and is this normal?
Thanks,E
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:28 AM . Last Modified: 2024-03-08 12:02 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:28 AM . Last Modified: 2024-03-08 12:02 AM
There are two cables that you can use.
940-0024C which is about 6 feet
http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=940%2D0024
or
AP9804 which is 15 feet
http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=AP9804
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:28 AM . Last Modified: 2024-03-08 12:02 AM
If you get the 0024C and it's not long enough, you can extend it with a standard back-to-back serial extender.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:28 AM . Last Modified: 2024-03-08 12:02 AM
Ok, just want to make sure I am not crazy here.
I plugged a serial cable on the back of a Smart-UPS 1400 to use to communicate with some software on a laptop in one of my racks.
When I plug the DB9 serial cable into the port on the UPS, the UPS completely shuts down and turns off.
I have to reset it and turn it back on.
Why would this happen and is this normal?
Thanks,E