Hello
Dears i'm facing this problem since today morning ! one of the A.Cs shows me alarm that is Compressor high Pressure Alarm>
so kindly guide me what should do ?
AC model is = ACRP102
ISX Central
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:21 AM . Last Modified: 2024-01-31 02:56 AM
Hello Altaleb.
The high head pressure alarm indicates a possible issue with the condenser. Check that there are no blown breakers for the condensing unit (outside unit) and that the fans are spinning. If this alarm has only happened once, reset the alarm on the unit and monitor it closely. If the alarm keeps happening or comes back, please call your local tech support for further troubleshooting to identify the exact issue.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:21 AM . Last Modified: 2024-01-31 02:56 AM
Hello Altaleb.
The high head pressure alarm indicates a possible issue with the condenser. Check that there are no blown breakers for the condensing unit (outside unit) and that the fans are spinning. If this alarm has only happened once, reset the alarm on the unit and monitor it closely. If the alarm keeps happening or comes back, please call your local tech support for further troubleshooting to identify the exact issue.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:21 AM . Last Modified: 2024-02-14 02:36 AM
thank you for your great support