Windows Server 2008 R2
Powerchute 2.1.1 will not uninstall. In Programs and Features, Powerchute reports "this item may already have been uninstalled. Do you want to remove the Program entry"
System restore is not a viable option on this production server.
Manual removal instructions would be appreciated so that I can upgrade to pcns310win-x86-64
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:49 AM . Last Modified: 2024-03-05 01:56 AM
Removed all registry entries as suggested.
Installed pcns3.1
Uninstalled pcns3.1 (required to remove the legacy PowerChute service)
Re-installed pcns3.1
Resolved. All systems working.
Many thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:49 AM . Last Modified: 2024-03-05 01:56 AM
Hi,
Sorry but PCNS 2.1.1 was discontinued more than 10 years ago so there is no documentation available for it. I suggest searching in the registry for APC, PCNS, PowerChute Network Shutdown and remove those entries. You should back the registry up first just in case you accidental remove something that causes a system issue. You can find instruction on how to back up the registry at Back up the registry - Microsoft Windows Help
Here is a list of registry entries PowerChute Network Shutdown (PCNS 3.x) creates. HKLM below stands for HKEY_LOCAL_MACHINE.
32-bit Registry Keys
Base Key: HKLM\Software\APC\PowerChuteNetworkShutdown\
Version: REG_SZ 3.0.0
ImagePath: REG_SZ
64-bit Registry Keys
Base Key: HKLM\Software\Wow6432Node\APC\PowerChuteNetworkShutdown\
Version: REG_SZ 3.0.0
ImagePath: REG_SZ
32-bit Service Registry Keys
Base Key: HKLM\SYSTEM\CurrentControlSet\Services\PCNS1
Description: REG_SZ Reliable network based shutdown of multiple servers.
DisplayName: REG_SZ PowerChute Network Shutdown
ErrorControl: REG_DWORD 0x00000001
ImagePath: REG_EXPAND_SZ
ObjectName: REG_SZ LocalSystem
Start: REG_DWORD 0x00000002 (2)
Type: REG_DWORD 0x00000110 (272)
64-bit Service Registry Keys
Base Key: HKLM\SYSTEM\CurrentControlSet\Services\PCNS1 WOW64 REG_DWORD 0x00000001 (1)
32-bit Uninstall Registry Keys
Base Key: HKLM\SOFTWARE\Microsoft\Windows\CurrentVersion\Uninstall\PowerChute Network Shutdown
DisplayIcon: REG_SZ
DisplayName: REG_SZ PowerChute Network Shutdown
DisplayVersion: REG_SZ 3.0.0
Publisher: REG_SZ APC by Schneider Electric
UninstallString: REG_EXPAND_SZ
URLInfoAbout: REG_SZ http://www.apc.com/support/
64-bit Uninstall Registry Keys
Base Key: HKLM\SOFTWARE\Wow6432Node\Microsoft\Windows\CurrentVersion\Uninstall\PowerChute Network Shutdown
DisplayIcon: REG_SZ
DisplayName: REG_SZ PowerChute Network Shutdown
DisplayVersion: REG_SZ 3.0.0
Publisher: REG_SZ APC by Schneider Electric
UninstallString: REG_EXPAND_SZ
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:49 AM . Last Modified: 2024-03-05 01:56 AM
Removed all registry entries as suggested.
Installed pcns3.1
Uninstalled pcns3.1 (required to remove the legacy PowerChute service)
Re-installed pcns3.1
Resolved. All systems working.
Many thanks