Hello Guys,
I trying to monitor the UPS using snmp but there are some missing mibs not working I don't know why ? can anyone support on this please
Sample MIBs
.1.3.6.1.4.1.318.1.1.1.2.2.4.0
1.3.6.1.4.1.318.1.1.1.3.2.1.0
1.3.6.1.4.1.318.1.1.1.4.2.2.0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:15 AM
Thanks a lot Gavan this will do the trick
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:05 AM . Last Modified: 2024-03-08 03:16 AM
Any Help please it's a little bit urgent
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:05 AM . Last Modified: 2024-03-08 03:16 AM
Hi Hasham,
Can you give us more detail on what your are trying to do?
The numbers your listed above are OIDs not MIBs, if you are looking for the correct MIB for the UPS then see below:
https://www.apc.com/shop/za/en/products/PowerNet-MIB-v4-3-2/P-SFPMIB432
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:05 AM . Last Modified: 2024-03-08 03:15 AM
Hello Gavan,
I will try to be more specific. I'm trying to monitor the UPS using centralized monitoring solution, one of the items I want to monitor is 1.3.6.1.4.1.318.1.1.1.2.2.4 (upsAdvBatteryReplaceIndicator)
when I use snmpwalk to get the return of this OID I got below error message
No such object available on this agent at this OID
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:05 AM . Last Modified: 2024-03-08 03:15 AM
Hi Hasham,
Not every OID in the MIB is applicable to every UPS.
If you provide me with a full SNMPWalk I can have a look, there may be an alternative that suits you UPS.
-Gavn
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:05 AM . Last Modified: 2024-03-08 03:15 AM
Hi Gavan
I used
snmpwalk -v2c -c public ups_ip 1.3.6.1.4.1.318.1.1.1.2.2.4
SNMPv2-AMI::enterprises.318.1.1.1.2.2.4 = No Such Object available on this agent at this OID
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:15 AM
Hi Hesham,
You could use:
.1.3.6.1.4.1.318.1.1.1.2.1.1
The status of the UPS batteries.
A batteryLow(3) value indicates the UPS will be unable to sustain the current load, and its services will be lost if power is not restored. A batteryInFaultCondition(4)value indicates that a battery installed has an internal error condition."
INTEGER { unknown ( 1 ) , batteryNormal ( 2 ) , batteryLow ( 3 ) , batteryInFaultCondition ( 4 ) }
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:15 AM
Hello Gavan,
Thanks a lot for you support, and please bear with me one last question, I need to monitor the operation mode, I mean I need to be alerted when the power cut off and the UPS starts to use the batteries
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:15 AM
Hi Hesham,
There's probably few ways to do it but I would recommend monitoring:
.1.3.6.1.4.1.318.1.1.1.2.2.1 - upsAdvBatteryCapacity
And then set an alert if the number decreases by more than x% or goes below 95% (depending on your situation)
Or you could monitor:
.1.3.6.1.4.1.318.1.1.1.3.2.4 - upsAdvInputFrequency
If the input frequency is 0hz then there is no power coming to the UPS.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:15 AM
Thanks a lot Gavan this will do the trick