APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
I have been upgrading my older APC's to newer SUMX 1500's with the AP9631 mgmt cards installed. Since putting the new UPS's in I get a lot of warm starts on these cards. I have turned the Sensitivity level to reduced. I have up dated the firmware to 5.1.3. I have left some of the unit on old version of the firmware. I have opened a case with APC and have got no where with them. Have anyone else had an issue with these new cards? Any ideas of how to solve the issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
I have been upgrading my older APC's to newer SUMX 1500's with the AP9631 mgmt cards installed. Since putting the new UPS's in I get a lot of warm starts on these cards. I have turned the Sensitivity level to reduced. I have up dated the firmware to 5.1.3. I have left some of the unit on old version of the firmware. I have opened a case with APC and have got no where with them. Have anyone else had an issue with these new cards? Any ideas of how to solve the issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
Incident: 100527-001319
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
hi
i looked this up and was dealing with the rep that was dealing with you. i see that we didnt get a response from you on this.
believe me - i know it is frustrating to deal with but we just want the most up to date information so that we can find a resolution to the problem.
warmstarts only mean that the card is rebooting briefly due to a configuration change, or other expected situations. in some situations though, it can happen but we don't know why.
i am actively working on these cases personally with our engineering team. it would be extremely helpful to access the card via FTP or SCP and see if there is a debug.txt in the /dbg directory to help us.
we also would need to confirm or deny if you only see this issue on AP9631 (versus AP9630) and if you have any accessories plugged into the RJ-45 UIO jacks on the back of the card. it appears you are only having it on (2) AP9631 cards in SMX1500RM2UNC units as far as I can tell.
has anything new developed in your case? we always appreciate up to date config.ini, event.txt and data.txt if you can provide them. you can attach them to the case if you want if you dont want to post them there but i cant stress that the more info we can get, the faster we get a resolution - as frustrating as it is. i hope you can understand..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
I will get updated info to you. Is there another email address I can contact you at with the update info?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
i will email you from my APC email the email address on your account is where you want it sent. if not, please PM me another email and I will email you directly.
thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
That is the correct email to reach me on thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
Hi, I have not received your email yet as we discussed yesterday.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
i sent an email yesterday at 4:57pm ET to the email in your profile. I did notice it was different than the one we have on file for APC tech support. I will try that one instead.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
I am having the same issue with random warmstarts.
Just installed a SMX1500RM2UNC with a AP9631 network card.
UPS:
Model: Smart-UPS X 1500
Serial Number: xxx
Firmware Revision: UPS 02.2 / COM 02.3 / UBL 05.0 / CBL 01.0
Manufacture Date: 02/25/2010
Apparent Power Rating: 1440 VA
Real Power Rating: 1200 W
Management Card:
Hardware Factory
Model Number: AP9631
Serial Number: xxx
Hardware Revision: 05
Manufacture Date: 04/29/2009
MAC Address: 00 C0 B7 4B B8 08
Management Uptime: 0 Days 7 Hours 52 Minutes
Application Module
Name: sumx
Version: v5.0.3
Date: Aug 6 2009
Time: 21:53:59
APC OS (AOS)
Name: aos
Version: v5.0.3
Date: Aug 4 2009
Time: 13:12:44
APC Boot Monitor
Name: bootmon
Version: v1.0.0
Date: Oct 8 2008
Time: 16:03:02
I FTP'd into it and there's nothing in the "dbg" folder.
The event log and data are attached.
Is there a solution to this?
Thanks
Brent
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:42 PM . Last Modified: 3 weeks ago
I have been upgrading my older APC's to newer SUMX 1500's with the AP9631 mgmt cards installed. Since putting the new UPS's in I get a lot of warm starts on these cards. I have turned the Sensitivity level to reduced. I have up dated the firmware to 5.1.3. I have left some of the unit on old version of the firmware. I have opened a case with APC and have got no where with them. Have anyone else had an issue with these new cards? Any ideas of how to solve the issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.