Hello,
question is asked often 😞
This AP9630 is displaying this message on 2 UPS. It's actually connected to Smart UPS 2200. If my doc is correct & up to date, it's running firmware UPS 09.4 (ID18).
Connected to serial to AP9630, Network Card AOS is v6.9.6, Smart-UPS & Matrix UPS APP v6.9.6 too.
Stat : P+ N4+ N6+ A!
I already tried the "resetToDef -p keepip". After about 10 minutes I was able to connect using putty again, setting correct IP, reboot. Wait 10 more minutes to get ping ok. I already was having this problem with firmware 6.9.4 and the upgrade didn't solve it.
What can I do now ?
Thanks,
Vincent
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:17 AM
hello,
I try to follow the procedure of the KB (https://www.apc.com/us/en/faqs/FA293874/) as well as this video:
https://www.youtube.com/watch?v=P2dsPffXKz8&t=52s
But I still can't get access to BootMonitor.
- I am using TeraTerm on the COM8 at 9600 speed. It does not want to synchronize at a higher speed.
- During the reboot, TeraTerm almost immediately displays the login prompt 'User Name:'
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
First you need to log into the device via SSH or Serial and enable FTP using this command:
ftp -S enable
Next you need to download the following files:
https://schneider-electric.box.com/s/2pwkj0c41rs2byumkyafpezkvjx1ya63
Connect to the NMC using FTP, I recommend the WinSCP client,
Upload "apc_hw05_bootmon_109.bin" to the root,
The NMC will reboot,
Reconnect via FTP,
Upload "apc_hw05_aos_696.bin" to the root,
The NMC will reboot,
Reconnect via FTP,
Upload "apc_hw05_sumx_696.bin" to the root,
The NMC will reboot for the final time
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
Hello, no more luck 😞
after first & second upload, the card boot really fast. Less than 10 pings to be up. After the last one, it tapes 10 min.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
that sounds about right, the last one take a bit longer to install.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
but still can connect with https.
SSH stat still display : P+ N4+ N6+ A!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
try these commands:
web -s enable
reboot
That should enable HTTPS but I'm not sure the application has uploaded correctly.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
no more luck using http or https 😞
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:17 AM
another idea ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:17 AM
The A! in the stat field means that the application hasn't loaded properly. ;
The only other things that come to mind are to make sure your on the same subnet as the NMC when updating or to follow this process below:
https://www.apc.com/us/en/faqs/FA293874/
It requires physical access to the card and a serial cable.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:17 AM
hello,
I try to follow the procedure of the KB (https://www.apc.com/us/en/faqs/FA293874/) as well as this video:
https://www.youtube.com/watch?v=P2dsPffXKz8&t=52s
But I still can't get access to BootMonitor.
- I am using TeraTerm on the COM8 at 9600 speed. It does not want to synchronize at a higher speed.
- During the reboot, TeraTerm almost immediately displays the login prompt 'User Name:'
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.