We have just replaced an out of warranty 2200RMI2U UPS with a new SMT2200RMI2UC UPS. The original UPS had a AP9619 network management card in it which were were planning to install in the new UPS however the plastic tabs on the new UPS do not line up with the slots in the faceplate of the management card. Is the AP9619 card compatible with our new UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:47 AM . Last Modified: 2024-03-08 04:06 AM
Hi,
A SMT Smart-UPS requires network management card AP9630, AP9631, AP9635, AP9640, or AP9641. The SMT Smart-UPS is not compatible with the AP9619. See Schneider Electric FAQ FA156573 for more information.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:47 AM . Last Modified: 2024-03-08 04:06 AM
Hi,
A SMT Smart-UPS requires network management card AP9630, AP9631, AP9635, AP9640, or AP9641. The SMT Smart-UPS is not compatible with the AP9619. See Schneider Electric FAQ FA156573 for more information.