These cards have been running fine for months. Now no one can log in. I get this error "Notice Someone is currently logged into the APC Management Web Server. Please try again later. " No one is logged in. How can I reset this? Can it be done remotely?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
Hello,
You can also telnet into the device and then log out, that should reboot the web interface. Then you should be able to log into the web interface.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
You should be able to reboot the management card by pressing in the small 'reset' button on teh front of the card. As part of the reboot, it will close any existing open connections, and you should not recieve that message anymore. If you continue to recieve that message after rebooting, you should verify theat there are no active serial connections to the card as local serial connections take priority over all other connections.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:17 AM
Telnet fix worked for me. 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
Hello,
You can also telnet into the device and then log out, that should reboot the web interface. Then you should be able to log into the web interface.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
The Telnet solution worked for me too. Thanks all!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
Dirtfoot was correct, I reset the cards and all is well again. Thanks for all the help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
You should be able to reboot the management card by pressing in the small 'reset' button on teh front of the card. As part of the reboot, it will close any existing open connections, and you should not recieve that message anymore. If you continue to recieve that message after rebooting, you should verify theat there are no active serial connections to the card as local serial connections take priority over all other connections.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
Thanks! It is at a remote site but we will have someine there latter today. I am wondering if someone did plug it into the serial port too. I will let you know as soon as I do.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:20 AM . Last Modified: 2024-03-08 12:17 AM
Because of our psycho auditors telnet is disabled. Wish they would live in the "real" world for once. ;-))
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:17 AM
The easy solution, click on the:
http://YOUR.APC.IP/logout.htm
PS: APC seems do not know timeout session on my software version
APC OS (AOS)
Name: aos
Version: v3.7.0
Date: 01/13/2009
Time: 14:17:08
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:17 AM
Telnet fix worked for me. 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:16 AM
The 3 main connection methods, Local, Telnet, and Web, are prioritized (in that order). You will usually only see that message if a higher priority connection has already been established.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:16 AM
Man you are a genius! this logout trick just did it on an older AP9617 3.3.4!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:16 AM
Worked like a charm....thanks!!!!
On 11/26/2011 8:43 AM, lotabi said:The easy solution, click on the:
http://YOUR.APC.IP/logout.htm
PS: APC seems do not know timeout session on my software version
APC OS (AOS)
Name: aos
Version: v3.7.0
Date: 01/13/2009
Time: 14:17:08
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:21 AM . Last Modified: 2024-03-08 12:16 AM
This worked for us. Thank you!