APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:15 AM . Last Modified: 2024-02-14 02:36 AM
I already have modbus network that connect couple of EGX 100 with NSX switches. Schneider Electric Power Logic V 6.0 monitor all EGX’s, and everything work just fine, but I would like to add all UPS ( Galaxy 7000 with 66123 network cards ) and STS ( Upsilon 600 A with 66061 jbus/modbus cards ) to this monitoring system. Did somebody make this connection?
Thanks in advance ,E
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:15 AM . Last Modified: 2024-01-31 02:56 AM
Hi,
66123 and 66061 Modbus card works with ETG100 without problems
Just remember that polarity are reversed
Example: on 66061 RS485 2 wires:
- switchs 4
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:15 AM . Last Modified: 2024-01-31 02:56 AM
Did you resolve the problem? i'm having a similar situation....
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:15 AM . Last Modified: 2024-01-31 02:56 AM
Hi,
66123 and 66061 Modbus card works with ETG100 without problems
Just remember that polarity are reversed
Example: on 66061 RS485 2 wires:
- switchs 4
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.