Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • Knowledge Center
  • :
  • Building Automation Knowledge Base
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49724members
Join Now
243181posts
Join Now

Building Automation Knowledge Base

  • « Previous
    • 1
    • 2
    • 3
    • …
    • 35
  • Next »
690 posts
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 35
  • Next »
Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Subscribe to RSS Feed
  • Invite a Friend
  • Print Knowledge Base
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 35
  • Next »
Showing articles with label Field Devices. Show all articles

Unable to set the time on a SE7000 controller

Issue The documentation shows how to set the CLOCK but the clock fails to work. The controller always displays the Alarm "SetClock" and the time at the default value " Monday" 12:00 AM Product Line EcoStruxure Building Expert, Field Devices Environment SE7000 Room Controller SE8000 Room Controller Cause The Real Time Clock in the SE7000 uses the 50/60hz AC frequency to operate, if the unit is powered from a DC power source the Real Time Clock will not function and the clock time will always display Monday 12:00. Resolution Power the SE7000 controller from an AC power source if the RTC is required. Note: SE8000 uses a different RTC chip and can be powered from either AC or DC and the time operates correctly.
View full article
Picard Product_Support
‎2018-09-06 10:16 AM

Last Updated: Admiral DavidChild Admiral 15 hours ago

Labels:
  • EcoStruxure Building Expert
  • Field Devices
533 Views

DC1100 / DC1400 Display corruption.

Issue DC1100 / DC1400 Displays two horizontal black lines when powered up. Product Line Field Device Environment DC1100 / DC1400 Discrete Controller. Cause Cold Start has not been performed. Cold Start has been performed incorrectly. Mains borne corruption has affected processor. Resolution Carry out Cold Start: Isolate Controller power supply. Press and hold down "Enter" and "Exit" buttons. Keep "Enter" and " Exit" buttons depressed while restoring power. Display should show "Self Test" and "Initiating System Variables" Release "Enter" and "Exit" buttons. Controller may then be programmed in accordance with Data Sheet instructions.   Or, if the controller is non-recoverable, the DC1100 and DC1400 units are now obsolete. However, there are several 3rd party companies offering refurbished units, these can be found by using a browser and searching e.g. DC1100 repairs.    
View full article
Picard Product_Support
‎2018-09-06 02:16 PM

Last Updated: Admiral DavidChild Admiral ‎2020-12-15 01:15 AM

Labels:
  • Field Devices
981 Views

Replacing a Controlli MVB actuator on a VMB valve Replacing a Controlli S300 Actuator

Issue The MVB actuator is no longer available from Schneider Electric Replacing a Controlli S300 Actuator Product Line Field Devices Environment VMB valves MVB actuators S300 actuator Cause Only the actuator requires replacing but the MVB is no longer available from Schneider Electric. Resolution Note: The MVB actuators are still manufactured by Controlli, but not distributed by Schneider Electric. Use the AG52 valve linkage kit 880-0129-000. For the Controlli MVB22, MVB26 and MVB28 or S300 replace with the MV15B-230 actuator For the Controlli MVB46 replace with the MV15B-24 actuator For the Controlli MVB32, MVB52 and MVB56 replace with the M800 880-0310-030 actuator If a D36 auxiliary switch was fitted in the  the MVB actuator or if the auxiliary switch was used in the S300 actuator then the following auxiliary switch packs can be used: M800, use the 880-0104-000 kit or order the M800-S2 880-0311-030 actuator which includes 2 auxiliary switches. MV15B-24/230, use the 880-0469-000 kit. Note: if the valve also requires replacing see VSB, VSB..F, VMB, VMB..F Schneider Electric replacement valves.
View full article
Picard Product_Support
‎2018-09-11 04:26 AM

Last Updated: Admiral DavidChild Admiral ‎2020-12-10 07:23 AM

Labels:
  • Field Devices
1174 Views

Temperature Sensor Resistance Charts

Issue Temperature Sensor Resistance Charts Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Temperature Sensors Cause Temperature (°C) to Resistance Charts (ohms). Upgrading the site BMS, but retaining the existing sensors and the sensor resistance values are not known. Resolution The resistance of a sensor at a specific temperature can be downloaded here. The devices covered are Schneider-Electric's range including Andover, TAC and Satchwell and other manufacturers temperature sensors. All are detailed below. For the standard thermistor, tables click here, where the INET, I/A, and BALCO resistance tables are detailed. This is the chart for the Precon Thermistors - ACCTemp 10K Type III thermistor also known as the 10K4A1 Thermistor. For EcoStruxure I/O Module universal inputs, the type of thermistor bead is classed as a: "10k Type I (Continuum)" Satchwell T range is now known as STR600, STP660, STD600, STO600 10K3A1 with shunt Drayton DC1000, DC1100 30K6A1 is now known as STR600D, STP600D, STO600D Andover 10K4A1 TAC Inc. Vista 1.8KA1 I/A series 10K3A1 with 11K shunt INET 10K2A1 (10k Dale) BALCO 1000 ohm RTD Older Satchwell ranges: Satchwell DW1204, DW1305, DWS1202 Satchwell DO Satchwell DD/DR Other manufacturers include: Allerton 3K3A1 Ambiflex 2012, Honeywell Aquatrol, Jel/Thorn, Trend, York 10K3A1 Schlumberger (air) 5K3A1 Schlumberger (immersion) 100K6A1 Automatrix, York, Sibe 10K4A1 Honeywell 20K6A Landis & Gyr PT100A, PT1000A For I/A Series Controllers (MNL/MNB) Compatible sensors that have a built-in 11k shunt resistor include the TS-5711-850, TS-57011-850, TS-57031-850, and TSMN-90110-850 Series. Any sensor that matches resistance to temperature curve for a 10K Thermistor Type G (U.S. Sensor), Type 9 (Dale/Vishay) or Type III (ACI Series AH) can be used with the I/A Series MNL and I/A Series MNB series controllers, provided that a 11k ± 0.1% 1/8 watt resistor is wired in parallel with the sensor. The input has a range of -10 to 135 °F (-23.3 to 57.2 °C) with an accuracy of ±1% of span. Temperature / Resistance Reference Values Temperature Deg F (Deg C) Resistance Resistance Incl. 11k Shunt 32 (0) 25490 8,012 68 (20) 12,260 5,798 75 (25) 10,000 5,238 104 (40) 5,592 3,707 140 (60) 2,760 2,206 The full temperature / resistance table for the US Sensor 10K Thermistor R-T Curve Type G sensor can be found here. Please note that the controller may not be able to use the full temperature range shown in the table.  
View full article
Picard Product_Support
‎2020-12-02 06:46 AM

on ‎2020-12-02 06:46 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell MicroNet
  • Satchwell Sigma
  • TAC IA Series
  • TAC INET
  • TAC Vista
6890 Views

Replacement of TAC TRV-S series Butterfly Valve Body by S-E VF208W series Butterfly Valve Body due to obsolescence.

Issue TAC TRV-S series Butterfly Valve Body requires replacement. Product Line Field Devices Environment TAC TRV-S series Butterfly Valve Body installations. Cause Obsolescence of TAC TRV-S series Butterfly Valve Body. Resolution Replace TAC TRV-S series Butterfly Valve Body with S-E VF208W series Butterfly Valve Body. Replace TAC MB15 / MB30 Actuator with S-E MF20 / MF40 series Actuator as appropriate. It should be noted that where a TAC TRV-S series Butterfly Valve Body is to be replaced by a S-E VF208W series Butterfly Valve Body the TAC Actuator fitted to the TAC TRV-S Butterfly Valve Body will not be suitable for reuse on the S-E VF208W.Buttterfly Valve Body. TAC TRV-S series Butterfly Valves utilise TAC MB15 / MB30 series Actuators. TAC MB15 / MB30 Actuators are not suitable for use on S-E VF208W series Butterfly Valve Bodies. S-E VF208W series Butterfly Valve Bodies utilise S-E MF20 / MF40 series Actuators. S-E MF20 / MF40 series Actuators are suitable for use on TAC TRV-S series Butterfly Valve Bodies, but then no linkage kit should be mounted. MF20 datasheet MF40 datasheet  
View full article
Picard Product_Support
‎2018-09-07 03:23 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-04 08:56 AM

Labels:
  • Field Devices
708 Views

Replacement of TAC VG211, VG222 and VG321 series Valve Bodies by S-E.VGS211F 15 and 100CS series Valve Bodies due to obsolescence.

Issue Obsolescence of TAC VG211, VG222, and VG321 series Valve Bodies. Product Line Field Devices Environment TAC VG211, VG222, and VG321 series Valve Body installations. Cause Obsolescence of TAC VG211, VG222, and VG321 series Valve Bodies. Resolution Replace TAC VG211 series Valve Body with S-E.VGS211F 15 – 100CS series Valve Body. It should be noted that a number of anomalies appear in the current issue of the Data Sheet describing the VGS211F 15 - 100CS range of 2-port Valve Bodies. The VGS211F 15-100CS Data Sheet includes two tables of information. A discrepancy appears in respect of the Kv value stated for the 50mm size Valve Body. The table of information on Page 1 of the Data Sheet displays a Kv value of 38 The table of information on Page 2 of the Data Sheet displays a Kv value of 40 The correct Kv value is 40 The type designation stated in the Data Sheet for this Valve Body is also incorrect. The type designation for this Valve Body should read VGS211F-50CS 40M SD00 Arrangements are currently in hand to correct these anomalies. NB The table on Page 1 of the earlier VG211 Data Sheet displayed a Kv value of 38 This value was also incorrect. The Kv value should have read 40 The VG222, VG222 and VG321 are no longer available, as it is replaced with the following: VG222 Valves will have the family name VG221F VG321 Valves will have the family name VG311F Please find the Product Announcement PA-00085 with the information.
View full article
Picard Product_Support
‎2018-09-07 05:06 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-04 08:52 AM

Labels:
  • Field Devices
856 Views

TS-8XXX and TS-9XXX 1,1000 Ohm Balco sensor, Fahrenheit resistance table.

Issue TS-8XXX and TS-9XXX 1,1000 Ohm Balco sensor, Fahrenheit resistance table. Product Line Field Devices Environment Field devices Balco temperature sensors Cause Reference for integration and calibration Resolution Download spreadsheet file of chart below.     Temp (°F) Resistance (Ohms) Temp (°F) Resistance (Ohms) Temp (°F) Resistance (Ohms) -50 760.816 50 956.9 150 1185.2 -49 762.6 51 959 151 1187.7 -48 764.4 52 961.2 152 1190.1 -47 766.2 53 963.3 153 1192.6 -46 768 54 965.4 154 1195 -45 769.9 55 967.6 155 1197.5 -44 771.7 56 969.7 156 1199.9 -43 773.5 57 971.8 157 1202.4 -42 775.3 58 974 158 1204.9 -41 777.1 59 976.1 159 1207.3 -40 779 60 978.3 160 1209.8 -39 780.8 61 980.5 161 1212.3 -38 782.6 62 982.6 162 1214.8 -37 784.5 63 984.8 163 1217.3 -36 786.3 64 986.9 164 1219.7 -35 788.2 65 989.1 165 1222.2 -34 790 66 991.3 166 1224.7 -33 791.9 67 993.5 167 1227.2 -32 793.7 68 995.6 168 1229.7 -31 795.6 69 997.8 169 1232.2 -30 797.5 70 1000 170 1234.7 -29 799.3 71 1002.2 171 1237.3 -28 801.2 72 1004.4 172 1239.8 -27 803.1 73 1006.6 173 1242.3 -26 804.9 74 1008.8 174 1244.8 -25 806.8 75 1011 175 1247.3 -24 808.7 76 1013.2 176 1249.8 -23 810.6 77 1015.4 177 1252.4 -22 812.5 78 1017.6 178 1254.9 -21 814.4 79 1019.8 179 1257.4 -20 816.3 80 1022 180 1260 -19 818.2 81 1024.2 181 1262.5 -18 820.1 82 1026.5 182 1265.1 -17 822 83 1028.7 183 1267.6 -16 823.9 84 1030.9 184 1270.2 -15 825.8 85 1033.2 185 1272.7 -14 827.7 86 1035.4 186 1275.3 -13 829.6 87 1037.6 187 1277.8 -12 831.5 88 1039.9 188 1280.4 -11 833.5 89 1042.1 189 1283 -10 835.4 90 1044.4 190 1285.6 -9 837.3 91 1046.6 191 1288.1 -8 839.3 92 1048.9 192 1290.7 -7 841.2 93 1051.1 193 1293.3 -6 843.1 94 1053.4 194 1295.9 -5 845.1 95 1055.7 195 1298.5 -4 847 96 1057.9 196 1301 -3 849 97 1060.2 197 1303.6 -2 850.9 98 1062.5 198 1306.2 -1 852.9 99 1064.8 199 1308.8 0 854.8 100 1067 200 1311.4 1 856.8 101 1069.3 201 1314 2 858.8 102 1071.6 202 1316.7 3 860.7 103 1073.9 203 1319.3 4 862.7 104 1076.2 204 1321.9 5 864.7 105 1078.5 205 1324.5 6 866.7 106 1080.8 206 1327.1 7 868.6 107 1083.1 207 1329.8 8 870.6 108 1085.4 208 1332.4 9 872.6 109 1087.7 209 1335 10 874.6 110 1090 210 1337.7 11 876.6 111 1092.3 211 1340.3 12 878.6 112 1094.7 212 1342.9 13 880.6 113 1097 213 1345.6 14 882.6 114 1099.3 214 1348.2 15 884.6 115 1101.6 215 1350.9 16 886.6 116 1104 216 1353.5 17 888.6 117 1106.3 217 1356.2 18 890.7 118 1108.7 218 1358.9 19 892.7 119 1111 219 1361.5 20 894.7 120 1113.3 220 1364.2 21 896.7 121 1115.7 221 1366.9 22 898.8 122 1118 222 1369.5 23 900.8 123 1120.4 223 1372.2 24 902.8 124 1122.8 224 1374.9 25 904.9 125 1125.1 225 1377.6 26 906.9 126 1127.5 226 1380.3 27 909 127 1129.9 227 1382.9 28 911 128 1132.2 228 1385.6 29 913.1 129 1134.6 229 1388.3 30 915.1 130 1137 230 1391 31 917.2 131 1139.4 231 1393.7 32 919.2 132 1141.7 232 1396.4 33 921.3 133 1144.1 233 1399.2 34 923.4 134 1146.5 234 1401.9 35 925.4 135 1148.9 235 1404.6 36 927.5 136 1151.3 236 1407.3 37 929.6 137 1153.7 237 1410 38 931.7 138 1156.1 238 1412.8 39 933.8 139 1158.5 239 1415.5 40 935.9 140 1160.9 240 1418.2 41 937.9 141 1163.4 241 1421 42 940 142 1165.8 242 1423.7 43 942.1 143 1168.2 243 1426.4 44 944.2 144 1170.6 244 1429.2 45 946.3 145 1173 245 1431.9 46 948.5 146 1175.5 246 1434.7 47 950.6 147 1177.9 247 1437.4 48 952.7 148 1180.3 248 1440.2 49 954.8 149 1182.8 249 1443         250 1445.7
View full article
Picard Product_Support
‎2018-09-07 05:03 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-04 08:47 AM

Labels:
  • Field Devices
872 Views

Replacement of obsolete Satchwell TR Series 230 V ac / 24 V ac Transformer by S-E TR Series 230 V ac / 24 V ac Transformer

Issue Satchwell TR Series 230 V ac / 24 V ac Transformer requires replacement. Product Line Field Devices Environment Satchwell TR1 (25VA), TR2 (50VA), TR3 (80VA), TR4 (200VA) and TR5 (300VA) 230 V ac / 24 V ac Transformers. Cause Obsolescence of Satchwell TR1, TR2, TR3, TR4 and TR5 230 V ac / 24 V ac Transformers. Resolution Replace Satchwell 871-1-201 TR1 (25VA) 230 V ac / 24 V ac Transformer with S-E TR 32 (32VA) 230 V ac / 24 V ac Transformer SE part number 3413032000. Replace Satchwell 871-1-202 TR2 (50VA) 230 V ac / 24 V ac Transformer with S-E TR 60 (60VA) 230 V ac / 24 V ac Transformer SE part number 3413060000. Replace Satchwell 871-1-203 TR3 (80VA) 230 V ac / 24 V ac Transformer with Transformer of another manufacturer's origin. Replace Satchwell 871-1-204 TR4 (200VA) 230 V ac / 24 V ac Transformer with Transformer of another manufacturer's origin. Replace Satchwell 871-1-205 TR5 (300VA) 230 V ac / 24 V ac Transformer with Transformer of another manufacturer's origin. The S-E TR range of Transformers provide the same functionality as the Satchwell TR range of Transformers but differ in appearance, dimensions and the range of VA ratings available. Specification EN 60742, with which the Satchwell range of Transformers complied, has been superseded by Specification EN 61558, with which the S-E range of Transformers comply. To review the transformer data sheet, see TR32-60 Transformer Data sheet en [101917].pdf.
View full article
Picard Product_Support
‎2018-09-07 02:58 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-30 10:48 AM

Labels:
  • Field Devices
957 Views

Replacement for Drayton A703 Immersion Temperature Sensor by S-E STP600D

Issue Replacement for Drayton A703 Immersion Temperature Sensor by S-E STP600D Product Line Field Devices Environment Drayton A703 Immersion Temperature Sensor installation. Cause Obsolescence of Drayton A703 Immersion Temperature Sensor Resolution 1.  Replace Drayton A703 Immersion Temperature Sensor with S-E STP600D The S-E STP600D provides the same functionality as the Drayton A703, differing only in its appearance and dimensions. The S-E STP600D Terminals are not polarised. N.B. It should be noted that the S-E STP600D is not supplied with a compatible Pocket. If it is not possible to utilise the existing Drayton Pocket, then a 100mm S-E Pocket (9121041000-Brass or 9121051000-Stainless Steel) should be selected as appropriate and in order to comply with the system requirements. There is a intentional gap between the top of the pocket, and the sensor housing, to ensure the probe tip touches the end of the pocket.  
View full article
Picard Product_Support
‎2018-09-07 04:26 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-30 10:47 AM

Labels:
  • Field Devices
571 Views

Replacement for temperature sensor TAC EGWP 120

Issue TAC EGWP 120 is obsolete and needs be replaced. Product Line Field Devices Environment 5122781000 TAC EGWP 120 5123106010 STP100-150 Cause Obsolete product needs replacement. Resolution TAC EGWP 120 (5122781000) is replaced by STP100-150 (5123106010)
View full article
Picard Product_Support
‎2018-09-06 09:37 AM

Last Updated: Admiral DavidChild Admiral ‎2020-10-13 02:13 AM

Labels:
  • Field Devices
593 Views

Replacements for Satchwell sensors

Issue Replacements for Satchwell sensors Product Line Satchwell MicroNet, Satchwell Sigma, Field Devices Environment DR DR3253 DRT DRT3451 DRT3453 DRT4453 DRT3651 DRT3652 DRT3801 DRT3851 DU DU4301 DUS DUS4302 DUSF DUSF4351 DUSF4352 DRTE DRTE2201 DRTE2801 DRTE2851 DRH DRH7702 DRH7703 DRTH DRTH7712 DRTH7713 DOT DOT0001 DOT0002 DOS DOS0002 DDT DDT1701 Cause Replacements for Satchwell Room sensors Resolution DOT0001/0002 Outside temperature sensor For CSC, KMC, MMC, IAC, MNN New part number: STO600/5126060000 DOS0002 Outside solar sensor For CSC, KMC, MMC, IAC, MNN New part number:  SSO600/5126050000 DR3253 Room sensor non-adjustable For SVT New part number: STR614/004604900 DRT3451 Room sensor exposed adjustment For CZU, CSC New part number: STR612/004604700 DRT3452 Room sensor concealed adjustment For CZU, CSC New part number: STR611/004604600 DRT3453 Room sensor non-adjustable CZU, CSC, CXR, CZT, KMC, MMC, IAC, MNN New part number: STR600/004604100 DRT4451 Room sensor non-adjustable As DRT 3453 in S-Link housing Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRT3651 Room temperature sensor exposed adjustment For CXR, CZT, KMC, MMC, IAC, MNN New part number: STR602/004604300 DRT3652 Room temperature sensor exposed + LED For MMC, IAC, MNN Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRT3801 Room temperature sensor fan switch On/off for CZU, MNN, IAC Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRT3851 Room temperature sensor fan speed switches As above plus medium and high Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DU4301 Room sensor temperature For MNN & URC New part number: STR601/004604200 DUS4302 Room sensor temperature setpoint advanced basic sensor New part number: STR613/004604800 DUSF4351 Room sensor temperature setpoint adjustable fan auto/on/off fan override New part number: STR609/004604400 DUSF4352 Room sensor temperature setpoint advanced fan Auto/1/2/3 fan override New part number: STR610/004604500 DRTE2201 Active room detector Basic sensor Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRTE2801 Active room detector On/off Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRTE2851 Active room detector Off/low/medium/high Obsolete with no Schneider Electric replacement Suggestions: Try Titan Products or Sontay DRH7702 2% 0-10V DC humidity only For KMC, MMC, IAC, MNN New part number: SHR100/006902340 DRH7703 3% 0-10V DC humidity only For KMC, MMC, IAC, MNN New part number: SHR100/006902340 DRTH7712 2% 0-10V DC humidity with Satchwell NTC TEMP OUTPUT For KMC, MMC, IAC, MNN New part number: SHR100-T6/006902420 DRTH7713 3% 0-10V DC humidity with Satchwell NTC temperature output For KMC, MMC, IAC, MNN New part number: SHR100-T6/006902420 DDT DDT1701, DDT1702 and DDT0001 Duct sensor non-adjustable New part number: STD660 5126030000 Contact Details: Titan Controls: http://www.titancontrols.net/ Sontay Controls https://www.sontay.com
View full article
Picard Product_Support
‎2020-09-29 10:29 AM

on ‎2020-09-29 10:29 AM

Labels:
  • Field Devices
  • Satchwell MicroNet
  • Satchwell Sigma
2152 Views

What is the BACnet MSTP unit load of the SpaceLogic SLP sensors

Issue What is the unit load of the SpaceLogic SLP Room Units that will help me to calculate how many SLP Room Units that can be added on ComA and ComB of a SmartX Server. Product Line EcoStruxure Building Operation, Field Devices Environment SpaceLogic SLP Room Unit SmartX Server Cause Documentation does not state the Unit Load (UL) of the SpaceLogic SLP Room Unit. Resolution The Generic application note AN01 can be applied with answers to the transceiver interface attributes below. The SpaceLogic SLP Room Unit range use the SN65HVD1781DR transceivers which are a failsafe transceiver (not requiring bias) and reduced 1/10 UL. In addition there are no local bias resistors and therefore the 1/10 UL of the transceiver would be the total UL presented to the bus by the SpaceLogic SLP Room Unit. Transceiver Xcvr Unit Load Xcvr Failsafe Adaptor Circuit Bias Circuit Bias Load Total Unit Load Isolated 485 Bus SN65HVD1781DR 0.1 Yes None None 0.1 No Based on the above the total number of devices can be calculated as 32/0.1 = 320. The BACnet MSTP standard specifies that the address range for BACnet master devices is 0-127 and therefore a SmartX Server is limited to 127 devices per com port (254 total per Server) so this should effectively be the limiting factor. Since the SpaceLogic SLP Room Unit does not have an isolated RS-485 interface it conforms to Generic RS-485 Network Device Configuration 1 in EBO Webhelp.  A network consisting of only SpaceLogic SLP Room Units should only require a 120 ohm termination resistor at each end of the bus and not require any bias resistors. Also check out the SmartStruxure-RS485-Controller Unit Load Quick-Help video on the Exchange.
View full article
Administrator CraigEl Administrator
‎2020-09-21 07:06 PM

Last Updated: Sisko Adam_Steele Sisko ‎2020-09-21 07:09 PM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
186 Views

How is a TC900 configured to use a 3-wire (floating) valve actuator?

Issue The documentation notes a TC900 can be changed from a 4-pipe system with a 2-wire motorized valve to a 2-pipe system with a 3-wire motorized valve. What parameter changes are required? Product Line Field Devices Environment TC907-3A4LAB TC907-3A4LMAB TC907-3A4DLSAB TC907-3A4DLMSAB TC907-4FMSAB TC907-3A4DPSAB TC907-3A4DPMSAB TC907-3A4DPMSA-24B TC907-4FMSA TC907-3A4LMA TC907-3A4LA TC907-3A4DPSA TC907-3A4DPMSA-24 TC907-3A4DPMSA TC907-3A4DLSA TC907-3A4DLMSA Cause Documentation is unclear in how a TC900 is configured to use a 3-wire valve actuator Resolution Access the parameter settings by pressing and holding the mode button for six seconds during thermostat power up. Press the mode button or Fan button to move forward or backward between the parameters until parameter 09 is displayed. Press the up and down buttons to set the parameter to 04.  
View full article
Administrator CraigEl Administrator
‎2020-09-09 12:48 AM

on ‎2020-09-09 12:48 AM

Labels:
  • Field Devices
140 Views

TA STL-SR Valves

Issue Replacement actuator for the STL-SR valve Product Line Field Devices Environment STL-SR Cause Replacement actuator for a STL-SR valve Resolution A M800 actuator or MV15B-24 or MV15B-230 actuator can be used to replace the actuator on the STL-SR valve series. Click here for the STL-SR datasheet. Notes: The original actuator e.g. M5CP, may have had a potentiometer fitted to provide position feedback to the controller. There is no direct replacement, the controller, actuator and valve may have to be changed. As a workaround, The M800 provides a 2-10V feedback, using a signal conditioner this could be converted to a resistive feedback. The original actuator may have had end switches fitted, order end switches to suit the replacement actuator. The M800 when used in floating control mode (dip switch 2= On) requires 4 wires. The original actuator used 3 wires to provide floating control.
View full article
Picard Product_Support
‎2018-09-11 07:11 AM

Last Updated: Admiral DavidChild Admiral ‎2020-08-06 02:42 AM

Labels:
  • Field Devices
604 Views

TC900 Modbus bias, termination and number of devices

Issue What is the unit load of a TC900 thermostat and what are the bias and termination requirements when used with a SmartX Server. Product Line EcoStruxure Building Operation, Field Devices Environment TC907-3A4LMA TC907-3A4DLMSA TC907-4FMSA TC907-3A4DPMSA TC907-3A4DPMSA-24 TC903-3A4LMA TC903-3A4DLMSA TC903-4FMSA TC903-3A4DPMSA TC903-3A4DPMSA-24 SmartX Server Cause Documentation does not state the RS-485 transceiver type for the TC900 range, making it unclear how many devices can exist under a SmartX servers RS-485 serial port ComA or ComB. Resolution Use the Worksheet for Configuration of RS-485 Bus with generic RS-485 devices on Webhelp to determine the appropriate Modbus configuration. The answers to the transceiver interface attributes below can be applied to complete the worksheet. Q1 Failsafe Receiver : The TC900 uses an RS-485 transceiver with an integrated idle-state failsafe receiver. Q2 Data Transmission Speed : TC900 thermostats can be configured to communicate at 4800, 9600, 19200 or 38400 bps. Q4 Isolated Interface : The TC900 does not provide an isolated RS-485 interface. Q6a Measured Resistance : With no electrical connections to the TC900, the measured resistance between the RS-485 low-side (-) signal and the communications common is 8.2K ohms. Based on this the unit load of the TC900 is 1.46 (12.000/8,200) Bias requirements and number of devices If there are only TC900 devices on the RS-485 bus then Generic RS-485 Network Device configuration 1 applies, configuration becomes very simple and no node or distance reductions are called for. The failsafe receivers can typically operate with no added bias resistors. Connect a 120 ohm termination resistor across the + and - data lines at the head end of the bus (typically at the SmartX server). Connect another 120 ohm termination resistor across the + and - data lines on the last node at the far end of the bus. Connect the shield drain wire to earth ground terminal rail in the panel with the SmartX server. This is the only ground connection of the shield for the complete cable segment. Connect the RET/Shield terminal (see the figure below) on the SmartX server to the ground rail in the panel using a 12 AWG (3.31 mm²) to 18 AWG (0.82 mm²) wire. Since the TC900 has a unit load of 1.4 the maximum number of devices that can be placed under each comm port using this configuration is 21 (31.5 / 1.46 = 21.5) Also check out the SmartStruxure-RS485-Controller Unit Load Quick-Help video on the Exchange.
View full article
Administrator CraigEl Administrator
‎2020-07-14 06:58 PM

Last Updated: Sisko Adam_Steele Sisko ‎2020-07-14 07:26 PM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
590 Views

Installation Guidelines for Electromagnetic Compatibility (EMC)

Issue Faulty operation of BMS equipment due to electrical interference from other equipment can be difficult and costly to identify and fix.  Guidance is required for the best installation practices to minimize the source of the interference and to protect against it when it occurs. Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, OTHER, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC Vista Environment All electrical equipment Cause Poor installation can cause equipment to generate high and low-frequency electromagnetic interference that can disrupt the operation of other systems. Resolution Schneider Electric has produced a document Practical Installation Guidelines which discusses the theory and offers practical guidelines to protect against and minimize the generation of, electromagnetic interference.
View full article
Picard Product_Support
‎2018-09-06 12:00 PM

Last Updated: Janeway RobertAndriolo Janeway ‎2020-06-30 09:17 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • OTHER
  • Pelco
  • Satchwell MicroNet
  • Satchwell Sigma
  • TAC IA Series
  • TAC Vista
1249 Views

GV sensor for use with TAC Xenta controller

Issue Can the GV sensor be connected to the TAC Xenta controller using Analog Input signal? Product Line TAC Vista, Field Devices Environment Xenta 401 Xenta 301 Xenta 281 Xenta 121 Xenta 122 Cause The GV sensor is non-electrical itself and needs a VAV controller to measure the air velocity transferred from the sensor. Resolution The 224V and 224VL that are listed in the GV documentation, are both obsolete and no longer available. The Xenta 102ES, part no. 007305370, is designed to work with the GV sensor.
View full article
Picard Product_Support
‎2018-09-06 12:27 PM

Last Updated: Sisko RandyDavis Sisko ‎2020-04-23 08:43 AM

Labels:
  • Field Devices
  • TAC Vista
632 Views

Replacement Satchwell pneumatic parts

Issue Replacement Satchwell pneumatic parts not available or obsolete and other pneumatic control brands e.g. Barber Colman used in the UK marketplace. Product Line Field Devices, Other Environment Pneumatics Part Number examples: 541, T100, 2212 Cause Replacement parts required. Resolution Contact OEM Comfort Telephone: +44 (0) 208-344 8777 Website: http://www.secureseal.com/ Email: lewin@secureseal.com
View full article
Picard Product_Support
‎2018-09-10 05:00 AM

Last Updated: Admiral DavidChild Admiral ‎2020-04-15 02:15 AM

Labels:
  • Field Devices
  • OTHER
741 Views

Using Windows Problem Steps Recorder

Issue Need to capture steps taken to reproduce a problem or a solution Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices, OTHER, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Windows 7 Windows 10 Windows Server 2008, 2012, 2016 Cause A series of screen captures will help to demonstrate the steps needed to reproduce a problem or a solution. You can use this tool to capture the steps you take as a problem occurs and send the output to someone so they can see a screenshot of each step. Resolution In Windows click on the Start menu button  Type "PSR" Windows 7 Windows 10, 2012, 2016 Open the Problem Steps Recorder Windows 7 Windows 10. 2012, 2016 Click Start Perform the desired tasks Click Stop Choose a location to save the file output The .zip file will contain a .mht file which can be opened in a web browser The screenshots will appear in order  This will be followed by a detailed output of keystrokes and mouse movements. For additional information please refer to Microsoft webpage on this topic: Record steps to reproduce a problem 
View full article
Picard Product_Support
‎2018-09-10 06:54 PM

Last Updated: Janeway RobertAndriolo Janeway ‎2020-03-26 05:04 PM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • OTHER
  • Satchwell MicroNet
  • Satchwell Sigma
  • TAC IA Series
  • TAC INET
  • TAC Vista
783 Views

TC300 Series Networking Digital Fan Coil Thermostat - Modbus Protocol Documentation

Issue TC300 Series Networking Digital Fan Coil Thermostat - Modbus Protocol Documentation Product Line Field Devices Environment TC300 Series Digital Fan Coil Thermostats Cause Modbus protocol information is needed in order to perform Modbus integration to the TC300 Series Digital Fan Coil Thermostats. Resolution The TC303 thermostats come with the option of Modbus communication for both 2- and 4-pipe configurations. Modbus is an open, widespread and well established serial communication protocol used within building automation. The support of Modbus communication allows simple integration of the TC303 thermostats to a building management system, using standard Modbus serial communications. The following models provide support for Modbus connectivity: TC303-3A2LM TC303-3A4LM TC303-3A2DLMS TC303-3A4DLMS TC303-3A2DPMS TC303-3A4DPMS The TC303 thermostats communicate as a Modbus RTU slave device over a serial RS-485 connection, allowing for the transfer of real time data. Thermostats manufactured from November 2018 (2018-W44-4)* onward can be configured to communicate at 9600 (default) or 4800 bps. The communication parameters for TC-300 thermostats manufactured prior to this date cannot be adjusted and are fixed as follows: 4800bps Baud Rate 8 Data Bits Odd Parity 1 Stop Bit The actual Modbus address of the thermostat can be set for each individual device on the RS-485 network. The address is defined via the parameter menu on the thermostat itself. The address range available is from 01 to 32 and is defined under menu item 04 of the parameter settings. For full details on this, other parameter setting options available and Modbus communications parameters/registers, please refer to the Installation Instructions.  Connection to the RS-485 network is made via dedicated terminals on the back of the thermostat and marked A (+) and B (-).   TC300 Series Digital Fan Coil Thermostat Installation Instructions TC300 Series Modulating Fan Coil Thermostat Installation Instructions   * Note - The Installation Instructions have not been updated to include the information that thermostats manufactured from November 2018 (2018-W44-4) onward can be configured to communicate at 9600 (default) or 4800 bps. 
View full article
Picard Product_Support
‎2018-09-10 11:04 AM

Last Updated: Janeway RobertAndriolo Janeway ‎2020-03-18 10:26 PM

Labels:
  • Field Devices
4102 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 35
  • Next »
Labels
  • Access Expert 81
  • Andover Continuum 2,168
  • Automated Engineering Tool 3
  • CCTV 53
  • EcoStruxure Building Expert 216
  • EcoStruxure Building Operation 1,465
  • EcoStruxure Workplace Advisor 1
  • Field Devices 690
  • OTHER 197
  • Pelco 1
  • Project Configuration Tool 19
  • Satchwell MicroNet 251
  • Satchwell Sigma 448
  • Security Expert 187
  • TAC IA Series 1,778
  • TAC INET 1,451
  • TAC Vista 2,040
  • « Previous
  • Next »
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric