Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • Knowledge Center
  • :
  • Building Automation Knowledge Base
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49466members
Join Now
242757posts
Join Now

Building Automation Knowledge Base

  • « Previous
    • 1
    • 2
    • 3
    • …
    • 35
  • Next »
690 posts
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 35
  • Next »
Sort by:
Helpfulness
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Subscribe to RSS Feed
  • Invite a Friend
  • Print Knowledge Base
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 35
  • Next »
Showing articles with label Field Devices. Show all articles

TS-8XXX and TS-9XXX 1,1000 Ohm Balco sensor, Fahrenheit resistance table.

Issue TS-8XXX and TS-9XXX 1,1000 Ohm Balco sensor, Fahrenheit resistance table. Product Line Field Devices Environment Field devices Balco temperature sensors Cause Reference for integration and calibration Resolution Download spreadsheet file of chart below.     Temp (°F) Resistance (Ohms) Temp (°F) Resistance (Ohms) Temp (°F) Resistance (Ohms) -50 760.816 50 956.9 150 1185.2 -49 762.6 51 959 151 1187.7 -48 764.4 52 961.2 152 1190.1 -47 766.2 53 963.3 153 1192.6 -46 768 54 965.4 154 1195 -45 769.9 55 967.6 155 1197.5 -44 771.7 56 969.7 156 1199.9 -43 773.5 57 971.8 157 1202.4 -42 775.3 58 974 158 1204.9 -41 777.1 59 976.1 159 1207.3 -40 779 60 978.3 160 1209.8 -39 780.8 61 980.5 161 1212.3 -38 782.6 62 982.6 162 1214.8 -37 784.5 63 984.8 163 1217.3 -36 786.3 64 986.9 164 1219.7 -35 788.2 65 989.1 165 1222.2 -34 790 66 991.3 166 1224.7 -33 791.9 67 993.5 167 1227.2 -32 793.7 68 995.6 168 1229.7 -31 795.6 69 997.8 169 1232.2 -30 797.5 70 1000 170 1234.7 -29 799.3 71 1002.2 171 1237.3 -28 801.2 72 1004.4 172 1239.8 -27 803.1 73 1006.6 173 1242.3 -26 804.9 74 1008.8 174 1244.8 -25 806.8 75 1011 175 1247.3 -24 808.7 76 1013.2 176 1249.8 -23 810.6 77 1015.4 177 1252.4 -22 812.5 78 1017.6 178 1254.9 -21 814.4 79 1019.8 179 1257.4 -20 816.3 80 1022 180 1260 -19 818.2 81 1024.2 181 1262.5 -18 820.1 82 1026.5 182 1265.1 -17 822 83 1028.7 183 1267.6 -16 823.9 84 1030.9 184 1270.2 -15 825.8 85 1033.2 185 1272.7 -14 827.7 86 1035.4 186 1275.3 -13 829.6 87 1037.6 187 1277.8 -12 831.5 88 1039.9 188 1280.4 -11 833.5 89 1042.1 189 1283 -10 835.4 90 1044.4 190 1285.6 -9 837.3 91 1046.6 191 1288.1 -8 839.3 92 1048.9 192 1290.7 -7 841.2 93 1051.1 193 1293.3 -6 843.1 94 1053.4 194 1295.9 -5 845.1 95 1055.7 195 1298.5 -4 847 96 1057.9 196 1301 -3 849 97 1060.2 197 1303.6 -2 850.9 98 1062.5 198 1306.2 -1 852.9 99 1064.8 199 1308.8 0 854.8 100 1067 200 1311.4 1 856.8 101 1069.3 201 1314 2 858.8 102 1071.6 202 1316.7 3 860.7 103 1073.9 203 1319.3 4 862.7 104 1076.2 204 1321.9 5 864.7 105 1078.5 205 1324.5 6 866.7 106 1080.8 206 1327.1 7 868.6 107 1083.1 207 1329.8 8 870.6 108 1085.4 208 1332.4 9 872.6 109 1087.7 209 1335 10 874.6 110 1090 210 1337.7 11 876.6 111 1092.3 211 1340.3 12 878.6 112 1094.7 212 1342.9 13 880.6 113 1097 213 1345.6 14 882.6 114 1099.3 214 1348.2 15 884.6 115 1101.6 215 1350.9 16 886.6 116 1104 216 1353.5 17 888.6 117 1106.3 217 1356.2 18 890.7 118 1108.7 218 1358.9 19 892.7 119 1111 219 1361.5 20 894.7 120 1113.3 220 1364.2 21 896.7 121 1115.7 221 1366.9 22 898.8 122 1118 222 1369.5 23 900.8 123 1120.4 223 1372.2 24 902.8 124 1122.8 224 1374.9 25 904.9 125 1125.1 225 1377.6 26 906.9 126 1127.5 226 1380.3 27 909 127 1129.9 227 1382.9 28 911 128 1132.2 228 1385.6 29 913.1 129 1134.6 229 1388.3 30 915.1 130 1137 230 1391 31 917.2 131 1139.4 231 1393.7 32 919.2 132 1141.7 232 1396.4 33 921.3 133 1144.1 233 1399.2 34 923.4 134 1146.5 234 1401.9 35 925.4 135 1148.9 235 1404.6 36 927.5 136 1151.3 236 1407.3 37 929.6 137 1153.7 237 1410 38 931.7 138 1156.1 238 1412.8 39 933.8 139 1158.5 239 1415.5 40 935.9 140 1160.9 240 1418.2 41 937.9 141 1163.4 241 1421 42 940 142 1165.8 242 1423.7 43 942.1 143 1168.2 243 1426.4 44 944.2 144 1170.6 244 1429.2 45 946.3 145 1173 245 1431.9 46 948.5 146 1175.5 246 1434.7 47 950.6 147 1177.9 247 1437.4 48 952.7 148 1180.3 248 1440.2 49 954.8 149 1182.8 249 1443         250 1445.7
View full article
Picard Product_Support
‎2018-09-07 05:03 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-04 08:47 AM

Labels:
  • Field Devices
864 Views

What is difference between valve rangeability and turndown ratio?

Issue What is difference between valve rangeability and turndown ratio? Environment Valves Cause Definition of the terms helps explain the flow outcomes. Resolution Rangeability - maximum controllable flow divided by minimum controllable flow. Turndown ratio - normal maximum system flow divided by minimum controllable flow. Rangeability is the inherent characteristic of the valve and turndown ratio is installed characteristic.
View full article
Picard Product_Support
‎2018-09-06 02:30 PM

Labels:
  • Field Devices
2186 Views

Can the A or B port of a mixing or diverting valve be capped to change the valve to a two-way valve?

Issue Can you cap the A port or B port of a mixing or diverting valve to change the valve to a two way (straight through) valve? Product Line Field Devices Environment VB-9313 series Cause Capping A port or B port of a mixing or diverting valve to change the valve to a two way (straight through) valve Resolution Schneider Electric does not recommend this modification for the VB-9313 series, because the valves are not equal percentage and therefore will not provide good control. The valve performs as a linear valve when both ports are utilized. These curves are not additive. Total flow is determined with both ports contributing. The valve will perform as a quick acting valve if the B port is plugged and a nominally linear valve if the A port is plugged. Additional problems that can occur are: Insufficient force to close off. Two way valves usually require high actuator forces to provide close off. Valves are not designed to be tight seating. Valves are rated ANSI III therefore flow leakage through the controlled coil can be expected. Flow direction through the valve can not be reversed. Flow must oppose the plug when closing. Flow aiding the plug may create hammer by causing the plug to overcome the actuator force and slam against the seat. When converted to a two way control valve for a variable flow system, 3-way valves tend to be extremely over-sized creating poor process control. After considering the pros and cons of making this type of modification, you may choose to proceed with this modification. The performance penalties should be less in chilled water applications and higher in hot water application.
View full article
Picard Product_Support
‎2018-09-06 02:29 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-06-05 01:22 PM

Labels:
  • Field Devices
1006 Views

Replacement of Satchwell ALE series Linear Actuator by S-E M800 Linear Actuator due to obsolescence. (Actuator Selection)

Issue Satchwell ALE series Linear Actuator requires replacement. Environment Satchwell ALE series Linear Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body.  Actuator type :- ALE series.  Cause Obsolescence of Satchwell ALE series Linear Actuator. Resolution Replace Satchwell ALE series Linear Actuator with S-E M800 Linear Actuator and Linkage Kit :-   Linkage kit to mount a M800 actuator to a Satchwell valve (MZ,MZF, VZ, VZF, VSF and MJF) = L2SV Replace ALE Actuator with M800 + L2SV combined part number 880-0650-000 Replace ALE with Auxilary Switch kit with M800-S2 + L2SV combined part number 880-0651-000 Just linkage kit = 880-0124-000 Just M800 = 880-0310-030 N.B.  Should the Satchwell ALE series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :-  S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000)   Particular care should be taken when selecting an S-E Forta M800 Actuator to replace an existing Satchwell ALE series Actuator. The S-E Forta M800 Actuator may be used to replace an existing Satchwell ALE series Actuator but it should be noted that where an existing Satchwell ALE series Actuator has been connected directly to a Satchwell Controller, an independent Transformer rated to provide the greater level of power required by a single S-E Forta M800 Actuator (50VA) will also be required. (e.g. S-E Transformer Type TR60)   Where an existing Satchwell ALE series Actuator has been connected via an independent Transformer, it is possible that the Transformer may have been rated to provide the level of power required by a single ALE series Actuator (9.5VA) only.   In such circumstances the existing independent Transformer may also require replacement by another independent Transformer, rated to provide the greater level of power required by a single S-E Forta M800 Actuator (50VA) (e.g. S-E Transformer Type TR60) Details of the Schneider Electric M800 Actuator may be viewed here Details of the Schneider Electric TR60 Transformer may be viewed here
View full article
Picard Product_Support
‎2018-09-07 06:43 AM

Labels:
  • Field Devices
1311 Views

What is the replacement for a Drayton Theta YBL1 Valve Body / Actuator assembly?

Issue The Drayton Theta YBL1 Valve Body / Actuator assembly is to be replaced. Environment Replacement Drayton Actuator Valve YBL1 Cause The Drayton Theta YBL1 Valve Body / Actuator assembly is obsolete. Resolution OVERVIEW The Drayton Theta YBL1 Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement. The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits. No Valve Body / Actuator assemblies are currently available in these sizes. Details of the YB Valve Body may be viewed here.   VALVE BODY REPLACEMENT To replace the YBL1 Valve Body the following is required:- S-E SatchwellMB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2") Details of the MB Valve Body may be viewed here.   ACTUATOR REPLACEMENT (6-WIRE INSTALLATION) The YBL1 Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :-  Terminal M1 – Open signal Terminal M2 – Close signal Terminal M3 – Common  Terminal M4 – 135 ohm Feedback Potentiometer – winding Terminal M5 – 135 ohm Feedback Potentiometer – wiper Terminal M6 – 135 ohm Feedback Potentiometer – winding Where 6 wires are connected to the YBL1 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here.   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here   IMPORTANT NOTE In such 6-wire installations not only will the YBL1 Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.   CONTROLLER REPLACEMENT The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller. Details of the CSC Controllers may be viewed here.   SENSOR REPLACEMENT Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate. Outside Air Temperature Sensor (STO 600) Contact Temperature Sensor (STC 600), or alternatively :- Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001) Room Temperature Sensor (STR 600) – OPTIONAL ONLY Details of the STO 600 Outside Air Temperature Sensor may be viewed here. Details of the STC 600 Contact Temperature Sensor may be viewed here. Details of the STP 660 Water Temperature Sensor may be viewed here. Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here. Details of the STR 600 Room Temperature Sensor may be viewed here.   N.B. ACTUATOR REPLACEMENT (3-WIRE INSTALLATION) Should only 3 wires be connected to a YBL1 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here.   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here In such 3-wire installations the YBL1 Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
View full article
Picard Product_Support
‎2018-09-10 12:13 AM

on ‎2018-09-10 12:13 AM

Labels:
  • Field Devices
785 Views

How to configure a schedule in an SE8000

Issue Unable to configure the schedule in SE8000 series thermostat. Product Line EcoStruxure Building Expert, Field Devices Environment SE8000 Cause The system is not following building occupancy and operation as needed Resolution Tap and hold the top middle of the screen and tap on lower right arrow of page 1/2 setup. There are seven different schedule setting screens, one for each day of the week. Each day can have different scheduled events. Options The options settings allow the Room Controller to function in Occupied or Unoccupied. Occupancy Command Local occupancy: occupancy is determined by local PIR or schedule, as configured under Occ. Source from the configuration menu. Schedule Type 7 days: Independent scheduling for each day 5+1+1 days: Weekdays scheduling and Independent Weekend scheduling for Saturday and Sunday 5+2 days: Weekdays scheduling and Weekend scheduling
View full article
Picard Product_Support
‎2018-09-10 09:49 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-30 08:09 AM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
944 Views

Controlli S300 Actuator

Issue Controlli S300 Actuator Environment Controlli S300 Actuator Cause Controlli S300 Actuator terminal details. Resolution L=Neutral L'=230Vac B=Close signal from thermostat or control device R=230V to thermostat or control device V=Open signal from thermostat or control device To test: Place a wire link between R and B, the valve actuator will close, place a wire link between R and V, the valve actuator will open. If a auxiliary switch kit D22 is fitted, this can be used to signal the boiler/pump to start if the installation was a domestic. For the actuator datasheet click here.
View full article
Picard Product_Support
‎2018-09-10 05:15 AM

Labels:
  • Field Devices
607 Views

SE 7300 override/°C-°F button choice.

Issue When defining configuration on SE7300 part no, your choice is between "0" (override) and "5" (possibility to change between °C and °F in interface). Environment SE7300 Cause its not possible to have both override and °C/°F feature Resolution When defining the part number, you will have to choose. The override feature is usually the preferred choice in industrial applications, while the °C/°F feature is used for Hotels and similar, where users are given the possibility to change unit of desired temperature.
View full article
Picard Product_Support
‎2018-09-06 12:51 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
674 Views

TC303 Time and Day of the Week Settings

Issue TC303 Time and Day of the Week Settings Environment TC303 Series Fan Coil Thermostat Cause The time and day displayed on the thermostat is incorrect Resolution Press and hold the M button on thermostat for approximately 3 seconds and the time's hour will start to blink. Use the Up/Down arrows to change the value. Press the M button again to switch the focus to minutes and the day of the week. 
View full article
Picard Product_Support
‎2018-09-06 07:29 AM

Labels:
  • Field Devices
692 Views

Difference between valves V211 and V211T

Issue Please define the difference between the V211 and V211T Environment V211 V211T Cause There are 2 different valves with similar characteristics, what differences are there, and why should I choose one or the other? Resolution V211 is equipped with flanged connections, while the V211T has internal threaded connections.
View full article
Picard Product_Support
‎2018-09-06 12:49 PM

Labels:
  • Field Devices
527 Views

TC 30* Thermostat Certificate of Conformity and Battery Safety/Transportation Information

Issue Safety information can be requested when distributing thermostats, particularly via airplane. Environment Room thermostat Cause Not all documentation is available to download. Resolution TC300 3AxL Series Low Voltage Certificate of Conformity TC300 3AxL Series Electromagnetic Compatibility Certificate of Conformity TC300 3AxLM-DLS-DLMS Series Low Voltage Certificate of Conformity TC300 3AxLM-DLS-DLMS Series Electromagnetic Compatibility Certificate of Conformity Battery material safety data sheet. Identification and classification report for air transport of goods.  
View full article
Picard Product_Support
‎2018-09-10 09:09 AM

Labels:
  • Field Devices
512 Views

CSC4201 CSC4202 CSC4301 CSC4302 Climatronic Compensator Controller display flashing.

Issue CSC4201 CSC4202 CSC4301 CSC4302 Climatronic Compensator Controller display flashing. Environment Satchwell CSC4201 CSC4202 CSC4301 CSC4302 Climatronic Compensator Controller Cause Manual Override Switch is set in a mode other than AUTO (Clock symbol) Resolution Reset Manual Override Switch to AUTO (Clock symbol) mode. N.B. Details of this and other Manual Override Switch mode options and associated selection / de-selection may be found in the CSC4201 CSC4202 CSC4301 CSC4302 Climatronic Compensator Data Sheet, a copy of which may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 07:03 AM

on ‎2018-09-10 07:03 AM

Labels:
  • Field Devices
523 Views

TC300 Series Networking Digital Fan Coil Thermostat - Modbus Protocol Documentation

Issue TC300 Series Networking Digital Fan Coil Thermostat - Modbus Protocol Documentation Product Line Field Devices Environment TC300 Series Digital Fan Coil Thermostats Cause Modbus protocol information is needed in order to perform Modbus integration to the TC300 Series Digital Fan Coil Thermostats. Resolution The TC303 thermostats come with the option of Modbus communication for both 2- and 4-pipe configurations. Modbus is an open, widespread and well established serial communication protocol used within building automation. The support of Modbus communication allows simple integration of the TC303 thermostats to a building management system, using standard Modbus serial communications. The following models provide support for Modbus connectivity: TC303-3A2LM TC303-3A4LM TC303-3A2DLMS TC303-3A4DLMS TC303-3A2DPMS TC303-3A4DPMS The TC303 thermostats communicate as a Modbus RTU slave device over a serial RS-485 connection, allowing for the transfer of real time data. Thermostats manufactured from November 2018 (2018-W44-4)* onward can be configured to communicate at 9600 (default) or 4800 bps. The communication parameters for TC-300 thermostats manufactured prior to this date cannot be adjusted and are fixed as follows: 4800bps Baud Rate 8 Data Bits Odd Parity 1 Stop Bit The actual Modbus address of the thermostat can be set for each individual device on the RS-485 network. The address is defined via the parameter menu on the thermostat itself. The address range available is from 01 to 32 and is defined under menu item 04 of the parameter settings. For full details on this, other parameter setting options available and Modbus communications parameters/registers, please refer to the Installation Instructions.  Connection to the RS-485 network is made via dedicated terminals on the back of the thermostat and marked A (+) and B (-).   TC300 Series Digital Fan Coil Thermostat Installation Instructions TC300 Series Modulating Fan Coil Thermostat Installation Instructions   * Note - The Installation Instructions have not been updated to include the information that thermostats manufactured from November 2018 (2018-W44-4) onward can be configured to communicate at 9600 (default) or 4800 bps. 
View full article
Picard Product_Support
‎2018-09-10 11:04 AM

Last Updated: Janeway RobertAndriolo Janeway ‎2020-03-18 10:26 PM

Labels:
  • Field Devices
4096 Views

Valve Flange Tables

Issue Valve Flange Tables Product Line Field Devices Environment Valves Flanged Gaskets Bolt holes PN rating PCD Cause What flanged tables are used with what valves? Resolution The PN of the valve and the valve size will indicate the diameter, PCD (Pitch Circle Diameter), number of bolt hole/size and bolt size and therefore size of flange and gasket. Download the flange tables for BS EN 1092 (metric), ANSI  (ASA) and BS10 or here for an alternative flange table document.
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Last Updated: Admiral DavidChild Admiral ‎2019-08-20 02:36 AM

Labels:
  • Field Devices
1237 Views

Software Support for Design 360 and Studio 360

Issue Technical support contact information for Design 360 and Studio 360 Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Design 360 Studio 360 Cause Design 360 or Studio 360 has issues requiring technical support assistance which is not provided by PSS. Resolution Schneider Electric Employees should contact PSS who will provide you with your Branch Administrator and Technical Expert contact information. Partners may contact Smartware directly for any support of the tool at: Email: techsupport@smartwaretech.com Phone: (716) 213-2222
View full article
Picard Product_Support
‎2018-09-10 10:33 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • OTHER
  • Satchwell MicroNet
  • Satchwell Sigma
  • TAC IA Series
  • TAC INET
  • TAC Vista
1130 Views

Belimo vs. Schneider Electric actuators part numbers

Issue Some actuators manufactured by Belimo are also available from Schneider Electric Environment Various Belimo Actuators: AF 230 AF 230-S AF 24 AF 24-S AF 24-SR LF 230 LF 24 LM 230 A LM 230 A-S LM 24 A LM 24 A-S LM 24 A-SR NM 230A NM 24A NM 24A-SR SM 230A SM 24A SM 24A-SR Various Schneider electric actuators, part no: 875-0000-010 875-0010-010 874-0000-010 874-0010-010 877-0000-010 875-0003-000 874-0003-000 875-1001-000 875-1003-000 875-1005-000 875-1007-000 875-1009-000 875-1011-000 875-1015-000 875-1019-000 875-1021-000 875-1025-000 875-1029-000   Cause Cross reference between various actuators of Belimo and Schneider Electric Resolution A cross reference table for these actuators can be found here (.xls).
View full article
Picard Product_Support
‎2018-09-06 11:28 AM

Labels:
  • Field Devices
927 Views

Installation Guidelines for Electromagnetic Compatibility (EMC)

Issue Faulty operation of BMS equipment due to electrical interference from other equipment can be difficult and costly to identify and fix.  Guidance is required for the best installation practices to minimize the source of the interference and to protect against it when it occurs. Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, OTHER, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC Vista Environment All electrical equipment Cause Poor installation can cause equipment to generate high and low-frequency electromagnetic interference that can disrupt the operation of other systems. Resolution Schneider Electric has produced a document Practical Installation Guidelines which discusses the theory and offers practical guidelines to protect against and minimize the generation of, electromagnetic interference.
View full article
Picard Product_Support
‎2018-09-06 12:00 PM

Last Updated: Janeway RobertAndriolo Janeway ‎2020-06-30 09:17 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • OTHER
  • Pelco
  • Satchwell MicroNet
  • Satchwell Sigma
  • TAC IA Series
  • TAC Vista
1247 Views

DC1100 or DC1400 not accepting 0112 passcode to clear alarms or to alter settings.

Issue DC1100 or DC1400 not accepting 0112 passcode to clear alarms or to alter settings. Environment DC1100 DC1400 Cause When the passcode 0112 is used to clear alarms or to alter settings, the code is not accepted. Resolution The controller will require coldstarting. 1. Using the setup menu and view settings, make a note of the settings of the controller. 2. Coldstart the controller by turning the power off, hold down the enter and exit buttons, power on and then release the buttons. The controller should re-initialise and will return to its default settings. 3. Reprogramme the controller with time and date, heating and HWS schedules, and any other parameter required in the set up menu. e.g. no of boilers, HWS linked etc. 
View full article
Picard Product_Support
‎2018-09-06 11:02 AM

Labels:
  • Field Devices
735 Views

MN-Sx, MN-SxHT sensors calibration

Issue MN-Sx, MN-SxHT sensors calibration Environment I/A Series MicroNet Sensors (MN-Sxxx series) Cause Sensor readings inaccurate Resolution 1. Calibration in WorkPlace Tech application program Calibrate the temperature and / or humidity offset in the Hardware Wizard. Enter a positive or negative offset value. For examples, -0.5 or 0.5. The WorkPlace Tech application has to be compiled and downloaded to the controller for the offset to take effect.   2. Calibration via sensor's Diagnostic Mode (only available in MN-S3xx, MN-S4xx, MN-S4xx-FCS, and MN-S5xx) To enter the sensor's Diagnostic Mode, press the Up and Down buttons simultaneously until the sensor enters the Diagnostic Mode. Press the Override button (while still in Diagnostic Mode). This will lead you to a display where you can enter an offset for sensor calibration. Allow the sensor to return to the normal display (takes about 30 seconds).
View full article
Picard Product_Support
‎2018-09-06 03:01 PM

Labels:
  • Field Devices
  • TAC IA Series
706 Views

SE7300 series BACnet controller does not come online in StruxureWare Building Operation

Issue SE7300 series BACnet controller does not come online in StruxureWare Building Operation if the communications address is greater then 127. Product Line EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices Environment StruxureWare Building Operation BACnet Cause The communications Address of SE7300 series BACnet controller can be set between 0 to 254. In StruxureWare Building Operation the highest address can be set only up to 127. Resolution Set the communication address less than or equal to 127 for SE7300 series BACnet controllers. Please refer to the Default Device ID / Device Instance of SE7000 series BACnet controllers to know the default Device ID / Device Instance of SE7000 series BACnet controllers.
View full article
Picard Product_Support
‎2018-09-11 03:49 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
875 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 35
  • Next »
Labels
  • Access Expert 81
  • Andover Continuum 2,167
  • Automated Engineering Tool 3
  • CCTV 53
  • EcoStruxure Building Expert 216
  • EcoStruxure Building Operation 1,465
  • EcoStruxure Workplace Advisor 1
  • Field Devices 690
  • OTHER 197
  • Pelco 1
  • Project Configuration Tool 19
  • Satchwell MicroNet 251
  • Satchwell Sigma 448
  • Security Expert 186
  • TAC IA Series 1,778
  • TAC INET 1,451
  • TAC Vista 2,040
  • « Previous
  • Next »
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric