Issue
When attempting to upgrade the firmware in an MNB-1000, this error appears:
"Error 7 updating firmware--cannot start bootloader".
It appears like the MNB-1000 is running for a short period and then resetting.
Product Line
TAC IA Series
Environment
I/A Series MNB 1000
Cause
On occasion, activity on the MSTP trunk will cause this error.
Resolution
- Access the MNB-1000 and disable the MSTP trunk.
- Attempt to upgrade the Plant controller again.