WorkPlace Tech lines will not connect to objects even with "Snap and Glue" enabled

Issue

Connection lines will not connect to some objects on the drawing, but will on other objects. The "Snap and Glue" feature was verified per Connecting lines in WorkPlace Tech stay red even when snapped to an object.

Product Line

TAC IA Series

Environment

  • WorkPlace Tech 5.x
  • Windows XP SP3
  • Visio 2003
  • Visio 2007

Cause

Objects are on the "back" layer.

Resolution

  1. Select objects or complete drawing
  2. Right click
  3. Select Shape > "Bring to Front"