Issue

Can Inovonics wireless equipment be used with Xenta Servers?

Environment

  • Xenta Servers
  • Xenta 511, 527, 555, 701, 711, 721, 731, 913

Cause

The Inovonics Frequency Agile product line which is compatible with the Xenta Server driver is being obsoleted by the manufacturer Inovonics at the end of 2011.

Resolution

If you have existing devices installed in the field then they should continue to work and function.

New installations should explore other options for wireless sensors due to unavailability from the manufacturer.

The ability to add a RS232 wireless Inovonics interface was removed from XBuilder beginning in version 5.1.8.