New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Building Automation Knowledge Base
cancel
Showing results for 
Show  only  | Search instead for 
Did you mean: 
Announcements
PSST, your community homepage is getting a new face - stay tuned and experience the change in few days

Which models of the SE7300 series room controllers can be used with the SC3000 series relay packs?

Issue

Which models of the SE7300 series room controllers can be used with the SC3000 series relay packs?

Product Line

EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices

Environment

SE7300 series Room Controllers

Cause

The SC3000 series relay packs allows existing line voltage wiring between the fan coil unit and temperature controller to be re-used. Only certain models of the SE7000 series room controllers can be used with the relay packs. 

Resolution

The SER7300 is used with the SC3000.
Refer to F-27797 SER7300 and SC3000 Series datasheet. Refer to the F-27777 SC3000 Series datasheet to select the appropriate relay pack for your application. 

SE7000 series Room Controllers documentation can be found on The Exchange Download Center. 
 

Tags (1)
No ratings