What type of remote/external sensor can be connected to a SE7000 series thermostat?

What type of remote/external sensor can be connected to a SE7000 series thermostat?

Issue

Installing a SE7652A5045P and want to add an outside air and supply air temperature sensor.  What type of sensor is accepted?

Environment

SE7000 series room controllers

Cause

Spec requirement

Resolution

The SE7000 series sensor can take any 10k ohm NTC thermistor (type 2).

For a temperature / resistance chart, see page 6 in this guide.

For a Schneider-Electric compatible sensor, see page 7.