Issue
How can you use Loytec's LPA software with the AS as the interface
Product Line
EcoStruxure Building Operation
Environment
Automation Server
Loytec LPA
Cause
A Loytec LPA can be a valuable troubleshooting tool to diagnose communication problems on a LON fieldbus.
Resolution
As the Automation Server uses Loytec's Lon chip, it is possible to use Loytec's LPA software over the Lon port on the AS.
You need a license to use the LPA software. You either need the "LPA-IP" or the "LPA-IP-SW" package depending on your setup. Here is a product overview on Loytec's home page. Here is a link to download the software. You need to create a free login in order to download software from Loytec's home page.
For help buying and registering the LPA software read LonTalk Protocol Analyzer Software License and Registration Steps
For general help on Lonworks troubleshooting read Troubleshooting LON Network Communication
For help troubleshooting Lon communication with TAC Xenta's, read Actions for reducing Bandwidth in a Vista network
There is a limitation when using LPA through an AS. Refer to Not all traffic on a segment is captured when using the LPA through an Automation Server
Please make sure that you have a LonWorks interface configured in the Automation Server before proceeding. You will also need to add a Local Node to the interface and to commission it.
1. Start the LPA software
2. Click on "Profile -> Network Interface..."
3. Click on "Remote LPA Assignment"
4. Click on "Add Device"
5. Enter the IP address of the AS, click on "Get Info" and click on "Add Device and Restart Search"
6. Select the StruxureWare device and click on "Assign/Add"
7. Select the interface you want to assign to the AS, and click "Assign"
8. With the interface assigned, click "OK"
9. Select the SmartStruxure interface and click "OK"
10. Now the LPA software is using the AS as interface
11. Start a new LPA log