Issue
The Xenta 104-A plug-in limits the temperature value input between 32°F and 104°F.
Environment
Xenta 104-A Plug-In
Lonmaker 3.1 or Lonmaker 3.2
NL220
Cause
The Xenta 104-A plug-in limits the temperature value input between 32°F and 104°F.
Resolution
In Vista follow these steps:
- Navigate to the Xenta 104-A controller.
- Browse down to the 8030 function block and find the nciDischAirMax SCPT.
- Type in the designed high discharge air temp value.