Unable to set Units on an AI created in StruxureWare Building Operation Menta Editor

Unable to set Units on an AI created in StruxureWare Building Operation Menta Editor

Issue

  • Unable to set Units on an AI created in Building Operation Menta Editor
  • The Units drop down list appears but is blank

Product Line

EcoStruxure Building Operation

Environment

  • SmartStruxure (all revisions)
  • Building Operation Menta Editor
  • Analog Input/Output

Cause

Menta Editor gets the units from Building Operation WorkStation. If the Menta Editor is launched from the Start menu, then there is no connection to WorkStation and units will not be displayed in Menta Editor. This is a known issue which will not be corrected.

Resolution

All Menta applications should be opened from within the Workstation:

  1. Right click on the "Programmable Xenta" object
  2. Select "Edit"