Unable to read any public signals from TAC Xenta 300/400/280 in a TAC Xenta 511, but SNVTs from TAC Xenta 100 controllers are fine.

Issue

Unable to read any public signals from TAC Xenta 300/400/280 in a TAC Xenta 511, but SNVTs from TAC Xenta 100 controllers are fine.

Environment

  • Xenta Programmables
  • Xenta 511
  • Xenta 100 series ASCs

Cause

The TAC Xenta 511 is not a member of the TAC Vista group.

Resolution

  1. Go to the System plug-in
  2. Choose LNS Network >Create group bindings.