Unable to Initialize Continuum Database following installing no SQL instance

Unable to Initialize Continuum Database following installing no SQL instance

Issue

After installing a new SQL server and installing CyberStation on a workstation PC, Database Initialization is unable to connect to the database.

Environment

  • SQL
  • CyberStation
  • WebClient
  • Continuum
  • Database Initialization
  • Change DB Owner

Cause

Database has not been assigned an owner.

Resolution

  1. In SQL Server Management Studio, highlight ContinuumDB.
  2. Right Click on ContinuumDB.
  3. Select "New Query"
  4. In the query field type SP_ChangeDBOwner 'Andover97'
  5. Run the query
  6. Once the query returns Success, you should be able to initialize the database.