Transitioning Continuum access control related objects into AccessXpert sub instance

Transitioning Continuum access control related objects into AccessXpert sub instance

Issue

Getting error 'One or more errors occurred' when transitioning Continuum access control related objects into AX sub instance.

OneOrMoreErrors.png

 

In the screenshot above, the tool is attempting to transition objects into the PSS sub-instance under the root instance.

 

SubInstance.png

Product Line

Access Expert

Environment

  • Access Expert Premise Software
  • Access Expert Hosted Software

Cause

The transition tool GUI is misleading in terms of where specific information should be entered. 

Resolution

Due to an issue in the tool, only the instance field should be populated, in the case of a sub-instance specify the name of the sub-instance in the 'Instance' field.

 

PSSWorks.png