Tooltip feature for TGML Graphics

Issue

Tooltip feature for TGML Graphics was hotfixed in Vista 5.0.3 (Hotfix 20) and was disabled later versions of TAC Vista based on customers requirement.

Refer to TPA-MALI-08-0007.01 for more details

Product Line

TAC Vista

Environment

TAC Vista 5.0.3 and later versions.

Cause

By default, the tooltip feature in TGML Graphics was removed.

Resolution

To enable the Tooltip option in TGML graphics following these steps:

  1. The Tooltip snippet is available under Snippets > Basic Functions > Tooltip. If the editor does not have this snippet, download the attached Tooltip.zip snippet.
  2. Close all the TGML windows and Install the tooltip snippet
  3. Open the TGML editor and you can find the tooltip snippet under My Snippets
  4. Drag and drop the tooltip snippet on to the graphic objects window to see the tooltip feature.
  5. After drag and drop the tooltip snippet on to the graphic, the Metadata – TooltipContainer will be added to the object properties.
  6. Tooltip will now be available for this graphics Object. Repeat steps 4 and 5 for each other graphics Object.