New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Building Automation Knowledge Base
cancel
Showing results for 
Show  only  | Search instead for 
Did you mean: 
Announcements

- Discover the Exchange Community Top members of November here!

Time synchronization in Xenta 28x, 30x, 401 base unit controllers.

Issue

Time synchronization in Xenta 28x, 30x, 401 base unit controllers.

Environment

  • Xenta programmable controllers
  • Xenta 281, 282, 283, 301, 302, 401, 401:B

Cause

NOTE: If the Lonworks network has not been properly commissioned & downloaded the tree will not properly communicate with the Vista Server. Check your network tree for asterisks to see if any downloads are required.

Resolution

Although the Vista Operator Unit (the PC) synchronizes the time of all of the controllers in the Vista database every 10 minutes, the group master (in the absence of an Operator Unit) only synchronizes once a day.

Tags (5)
Labels (1)
No ratings