Time synchronization done by TAC Xenta 28x, 30x, 401 controllers.

Time synchronization done by TAC Xenta 28x, 30x, 401 controllers.

Issue

Will a TAC Xenta 28x, 30x, 401 controllers do time synchronization in the Lon network?

Product Line

TAC Vista

Environment

  • Xenta 401
  • Xenta 281/282
  • Xenta 301/302

Cause

The TAC Vista server will synchronize the time of all of the TAC Xenta controllers in the Vista database every 10 minutes by default but the time can be changed by a value greater than the Delta time setup in the Vista database and an update forced.

Vista time Sync.JPG

Resolution

The TAC Xenta group master will send out the time to all TAC Xenta devices in the group once a day and this time interval cannot be changed.

If the time in the TAC Xenta Master is changed for example by the OP-panel it will send out the time to all TAC Xenta devices in its network.