Issue
Do I have to install the Continuum Reports "add-on" for versions 1.7 or higher?
Environment
Continuum Reports
Cause
Continuum supplies many Report templates that include attractive bar-chart templates, pie-chart templates, and trend templates - giving Reports a customized "look and feel." To use these templates (and thus, reports in general) you must import them during the Continuum installation process, in version 1.7 or higher.
Resolution
It is not necessary to install report add-ons for versions 1.7 or higher because this is done during the installation procedure.
In the Database Initialization dialog, check the Create/Update Graphical Report Settings checkbox. (For more information, please see the Continuum Installation Guide, 30-3001-720.) If you do not check this checkbox then reports are not available.