The status of a Forced BACnet value is not reflected in a Graphic or the Watch Window

The status of a Forced BACnet value is not reflected in a Graphic or the Watch Window

Issue

The status of a Forced BACnet value is not reflected in a Graphic or the Watch Window.

Forced point indicator.png

Product Line

EcoStruxure Building Operation

Environment

  • Enterprise Server (ES)
  • Automation Server (AS)

Cause

This is functioning as designed.

It was designed so that the "Forced" status for BACnet values would not be displayed in graphics or the watch window.

Resolution

It was designed so that the "Forced" status for BACnet values would not be displayed in graphics or the watch window.

For a workaround using a PE Script program to show the forced icon for a BACnet value see How to show the forced icon for a BACnet value in a Graphic.

In EBO version 3.0.1 and later this issue only occurs on internal BACnet points, points which are located in the Application folder under the BACnet interface for the SmartX server.