Issue
TS-7222 and TS-6722 30K thermistor sensor (no 11K shunt) resistance table
Environment
- TS-7222
- TS-6722
Cause
Specification on the sensing element.
Resolution
Temp (°C) | Temp (°F) | Ohms |
25.0° | 77.0° | 30,000 |
26.0° | 78.8° | 28,806 |
27.0° | 80.6° | 27,678 |
28.0° | 82.4° | 26,598 |
29.0° | 84.2° | 25,566 |
30.0° | 86.0° | 24,582 |
31.0° | 87.8° | 23,637 |
32.0° | 89.6° | 22,737 |
33.0° | 91.4° | 21,873 |
34.0° | 93.2° | 21,048 |
35.0° | 95.0° | 20,256 |
36.0° | 96.8° | 19,500 |
37.0° | 98.6° | 18,774 |
38.0° | 100.4° | 18,081 |
39.0° | 102.2° | 17,415 |
40.0° | 104.0° | 16,776 |
41.0° | 105.8° | 16,167 |
42.0° | 107.6° | 15,582 |
43.0° | 109.4° | 15,021 |
44.0° | 111.2° | 14,481 |
45.0° | 113.0° | 13,965 |
46.0° | 114.8° | 13,470 |
47.0° | 116.6° | 12,993 |
48.0° | 118.4° | 12,537 |
49.0° | 120.2° | 12,099 |
50.0° | 122.0° | 11,679 |
51.0° | 123.8° | 11,274 |
52.0° | 125.6° | 10,887 |
53.0° | 127.4° | 10,515 |
54.0° | 129.2° | 10,155 |
55.0° | 131.0° | 9,813 |
56.0° | 132.8° | 9,480 |
57.0° | 134.6° | 9,162 |
58.0° | 136.4° | 8,856 |
59.0° | 138.2° | 8,562 |
60.0° | 140.0° | 8,280 |
61.0° | 141.8° | 8,007 |
62.0° | 143.6° | 7,746 |
63.0° | 145.4° | 7,494 |
64.0° | 147.2° | 7,251 |
65.0° | 149.0° | 7,017 |
66.0° | 150.8° | 6,792 |
67.0° | 152.6° | 6,573 |
68.0° | 154.4° | 6,366 |
69.0° | 156.2° | 6,165 |
70.0° | 158.0° | 5,970 |
71.0° | 159.8° | 5,784 |
72.0° | 161.6° | 5,604 |
73.0° | 163.4° | 5,430 |
74.0° | 165.2° | 5,262 |
75.0° | 167.0° | 5,100 |
76.0° | 168.8° | 4,944 |
77.0° | 170.6° | 4,794 |
78.0° | 172.4° | 4,650 |
79.0° | 174.2° | 4,509 |
80.0° | 176.0° | 4,374 |
81.0° | 177.8° | 4,242 |
82.0° | 179.6° | 4,116 |
83.0° | 181.4° | 3,996 |
84.0° | 183.2° | 3,879 |
85.0° | 185.0° | 3,765 |
86.0° | 186.8° | 3,654 |
87.0° | 188.6° | 3,549 |
88.0° | 190.4° | 3,447 |
89.0° | 192.2° | 3,348 |
90.0° | 194.0° | 3,252 |
91.0° | 195.8° | 3,159 |
92.0° | 197.6° | 3,069 |
93.0° | 199.4° | 2,982 |
94.0° | 201.2° | 2,898 |
95.0° | 203.0° | 2,817 |
96.0° | 204.8° | 2,739 |
97.0° | 206.6° | 2,661 |
98.0° | 208.4° | 2,589 |
99.0° | 210.2° | 2,517 |
100.0° | 212.0° | 2,448 |
101.0° | 213.8° | 2,382 |
102.0° | 215.6° | 2,319 |
103.0° | 217.4° | 2,256 |
104.0° | 219.2° | 2,196 |
105.0° | 221.0° | 2,138 |
106.0° | 222.8° | 2,081 |
107.0° | 224.6° | 2,026 |
108.0° | 226.4° | 1,973 |
109.0° | 228.2° | 1,921 |
110.0° | 230.0° | 1,871 |
111.0° | 231.8° | 1,822 |
112.0° | 233.6° | 1,775 |
113.0° | 235.4° | 1,729 |
114.0° | 237.2° | 1,685 |
115.0° | 239.0° | 1,642 |
116.0° | 240.8° | 1,600 |
117.0° | 242.6° | 1,560 |
118.0° | 244.4° | 1,520 |
119.0° | 246.2° | 1,482 |
120.0° | 248.0° | 1,445 |
121.0° | 249.8° | 1,409 |