Summary page or List of All Forced Variables in version 1.4.1 and older

Summary page or List of All Forced Variables in version 1.4.1 and older

Issue

Search of All Forced Variables

Environment

StruxureWare Building Operation site

Cause

Desire to search of All Forced Variables without having to visit and physically look at each point.

Wanting a Summary page that is not in the Reports Server, but on the AS or ES which shows which points are Forced and which are not Forced.

Resolution

Forced Values can be found in system tree. Example with screen shot below: ES/Servers/AS/System/Modules/RuntimeDBManager/VariableManager/Variables if you enabled the isForced column.