Some users are unable to see I/NET values on a graphics page displayed in a 527

Some users are unable to see I/NET values on a graphics page displayed in a 527

Issue

Some users are unable to see I/NET values on a graphics page displayed in a 527

Environment

Xenta 527

TGML

Cause

User permissions on the 527 must allow the user to access the I/NET links that are being displayed

Resolution

  1. Log out of the 527
  2. Log in as the root user
  3. In the Configuration folder, select User administration
  4. Modify the user that was having issues.
  5. Click on the ".." link at the top of the folder list till you are in the root folder
  6. Click on the "inet" link to modify permissions of the I/NET folder
  7. Give the user read and read/write access
  8. Save changes