Issue
After installing SigmaX version 5.0 or later, when running the software an error message reports a missing DLL.
Environment
SigmaX version 5.0, 5.2, 6.01, and 6.02
Cause
System Path variable is missing C:\Sigma\Bin
Resolution
Make the following modification to the PC's System Properties. Note: This addition is only required on machines running SigmaX.
- Right click the My Computer icon on the desktop and select Properties
- Choose the Advanced tab and select the Environment Variables button
- From the System Variables section, highlight Path and select Edit
- The statement ‘;C:\Sigma\Bin’ must be added to the end of the Variable value line