Sigma BAS PIU error messages

Sigma BAS PIU error messages

Issue

BAS terminal receives system messages from a PIU with no explanation and is asked to contact Product Support. For example "Message No. 19920 not available. Please contact Product Support"

Product Line

Other, Satchwell Sigma

Environment

  • BAS PIU  and Sigma Pre-release 4 System Messages
  • BAS (1 - 10499)
  • SNP Gateway ( 10500-10999 )
  • CHUBB Remote Access Management ( 11000-11499 )
  • CEGELEC ( 11500-11999 )
  • OTIS   ( 12000-12499 )
  • CCURE ( 12500-12999 )
  • WORMALD ( 13000-13499 )
  • ASIC ( 13500-14999 )
  • SIMPLEX ( 14000-14499 )
  • CARRIER DATAPORT  ( 14500-14499 )
  • EXPRESS LIFT ( 15000-15499 )
  • CARDKEY ( 15500-15999 )
  • Mitsubishi ( 16000-16499 )
  • Liebert ( 16500-16999 )
  • IMPACC ( 17000-17499 )
  • YORK ( 18000-18499 )
  • AUTOFLAME (19000 - 19100)
  • AUTOMETERS (19100-19199)
  • MITSUBISHI PLC (19200 - 19299)
  • SIEBE MICRONET (19400 - 19499)
  • CROWCON (19500 - 19599)
  • MNI (MicroNet Interface) ( 19700-19799 )
  • Colt OPV ( 19800-19899 )
  • MODBUS ( 19900-19999 )
  • MCQUAY (20000 - 20199)
  • FIDELIO (20200 - 20299)
  • ATLAS COPCO ( 20301-20399 )
  • UNIFACT PRO ( 20500-20599 )

Cause

Due to a size limit (64Kb) not all the PIU error messages are included in the Messages.ini file.

Resolution

A more complete list of the of BAS error messages can be found here.

  1. Copy the appropriate section
  2. Paste into the C:\Bas\Data\Messages.ini file into the correct sequence as by message number
  3. The maximum size of the message.ini file must not exceed 64Kb

Example:

example.PNG