Issue
- Setpoint adjustment using a physical input doesn't work on the Xenta 121.
- Effective Setpoint has a value of 95°F
Environment
- ZBuilder 4.xx - 5.0.1
- Xenta 121-HP
- Xenta 121-FC
Cause
A problem in ZBuilder improperly adjusted the Temperature Offset Wheel Scaling units.
Resolution
- Upgrade to Zbuilder 5.0.2 or higher
-
Manually change the SCPTmaxRemoteTempSetpoint and SCPTminRemoteTempSetpoint using the following formula
Degrees offset * 1.8 + 32
All values should be entered as positive.
Example:
2 degrees up and 5 down results in a maxRemoteTempSetpoint of 35.6 and minRemoteTempSetpoint of 42.8.