Security Expert Reader Formats are Greyed Out

Issue

It is not possible to change Primary or Secondary Reader Formats as they are greyed out.

edit2.png

Product Line

Security Expert

Environment

Client/Server

Cause

If the Reader Expander Port Network Type is set to Schneider Electric RS485 the option to change the format on that Expander Reader 1 or Reader 2 Tab is edit locked.

edit1.png

Resolution

Under the General Tab change the Port 1 Network Type to Wiegand

edit3.png

 Under the Reader 1 Tab the Reader's Primary and Secondary Formats can now be changed

edit6.png

Repeat process for Reader Expander Port 2 Network Type and Reader 2 Primary and Secondary Formats as required.

Remember under the General tab to change the Network Port Types back to Schneider Electric RS485 before saving.