SQL Host not passing data to Xenta 527 Web Server

SQL Host not passing data to Xenta 527 Web Server

Issue

SQL Host not passing data to Xenta 527 Web Server

Product Line

TAC INET, TAC Vista

Environment

I/NET

527 Web Server

Cause

When defining the Host for the primary SQL server, you have options of 1-250. When using a Web Server to send this information to a Vista System you must define the primary SQL server with a Host number less than 63.

Resolution

  1. In I/NET configuration, define the primary SQL server's Host number between 1 and 63
  2. Restart the I/O server
  3. Connect to each Xenta 527 Web Server on site and modify change the SQL Host # to the host number assigned in step 1
  4. Restart each 527