Issue
SE8000 series room controller - BACnet max master setting
Environment
StruxureWare Building Operation Automation Server BACnet MS/TP integration to SE8000 (BACnet) room controller
Cause
The BACnet max master setting is not available to be set locally on the SE8000 room controller
Resolution
The max master setting of the SE8000 can be changed in EcoStruxure Building Operation Workstation.
- Add the SE8000 to the SmartStruxure Server
- Open the SE8000 device properties
- On the Advanced tab, change the Maximum master property (which is a read/write property) to the required value.