SE7300 series BACnet controller does not come online in StruxureWare Building Operation

Issue

SE7300 series BACnet controller does not come online in StruxureWare Building Operation if the communications address is greater then 127.

Product Line

EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices

Environment

  • StruxureWare Building Operation
  • BACnet

Cause

The communications Address of SE7300 series BACnet controller can be set between 0 to 254. In StruxureWare Building Operation the highest address can be set only up to 127.

Resolution

Set the communication address less than or equal to 127 for SE7300 series BACnet controllers.

Please refer to the Default Device ID / Device Instance of SE7000 series BACnet controllers to know the default Device ID / Device Instance of SE7000 series BACnet controllers.