Replacing a Controlli MVB actuator on a VMB valve Replacing a Controlli S300 Actuator

Replacing a Controlli MVB actuator on a VMB valve Replacing a Controlli S300 Actuator

Issue

The MVB actuator is no longer available from Schneider Electric

Replacing a Controlli S300 Actuator

Product Line

Field Devices

Environment

  • VMB valves
  • MVB actuators
  • S300 actuator

Cause

Only the actuator requires replacing but the MVB is no longer available from Schneider Electric.

Resolution

Note: The MVB actuators are still manufactured by Controlli, but not distributed by Schneider Electric.

  1. Use the AG52 valve linkage kit 880-0129-000.
  2. For the Controlli MVB22, MVB26 and MVB28 or S300 replace with the MV15B-230 actuator
    For the Controlli MVB46 replace with the MV15B-24 actuator
    For the Controlli MVB32, MVB52 and MVB56 replace with the M800 880-0310-030 actuator
  3. If a D36 auxiliary switch is used in the MVB actuator or if a S300 actuator was fitted then use the following:
    M800, use the 880-0104-000 kit, or order the M800-S2 880-0311-030 actuator which includes 2 auxiliary switches.
    MV15B-24/230, use the 880-0469-000 kit. 

Note: if the valve also requires replacing see VSB, VSB..F, VMB, VMB..F Schneider Electric replacement valves.