  • Replacements for Satchwell sensors
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49470members
Join Now
242766posts
Join Now

Replacements for Satchwell sensors

Back to Building Automation Knowledge Base
Options
  • Article History
  • Subscribe to RSS Feed
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2143 Views
Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacements for Satchwell sensors

Picard Product_Support
‎2020-09-29 10:29 AM

on ‎2020-09-29 10:29 AM

Issue

Replacements for Satchwell sensors

Product Line

Satchwell MicroNet, Satchwell Sigma, Field Devices

Environment

DR

  • DR3253

DRT

  • DRT3451
  • DRT3453
  • DRT4453
  • DRT3651
  • DRT3652
  • DRT3801
  • DRT3851

DU

  • DU4301

DUS

  • DUS4302

DUSF

  • DUSF4351
  • DUSF4352

DRTE

  • DRTE2201
  • DRTE2801
  • DRTE2851

DRH

  • DRH7702
  • DRH7703

DRTH

  • DRTH7712
  • DRTH7713

DOT

  • DOT0001
  • DOT0002

DOS

  • DOS0002

DDT

  • DDT1701

Cause

Replacements for Satchwell Room sensors

Resolution

DOT0001/0002

  • Outside temperature sensor
  • For CSC, KMC, MMC, IAC, MNN
  • New part number: STO600/5126060000

DOS0002

  • Outside solar sensor
  • For CSC, KMC, MMC, IAC, MNN
  • New part number:  SSO600/5126050000

DR3253

  • Room sensor non-adjustable
  • For SVT
  • New part number: STR614/004604900

DRT3451

  • Room sensor exposed adjustment
  • For CZU, CSC
  • New part number: STR612/004604700

DRT3452

  • Room sensor concealed adjustment
  • For CZU, CSC
  • New part number: STR611/004604600

DRT3453

  • Room sensor non-adjustable
  • CZU, CSC, CXR, CZT, KMC, MMC, IAC, MNN
  • New part number: STR600/004604100

DRT4451

  • Room sensor non-adjustable
  • As DRT 3453 in S-Link housing
  • Obsolete with no Schneider Electric replacement
  • Suggestions: Try Titan Products or Sontay

DRT3651

  • Room temperature sensor exposed adjustment
  • For CXR, CZT, KMC, MMC, IAC, MNN
  • New part number: STR602/004604300

DRT3652

  • Room temperature sensor exposed + LED
  • For MMC, IAC, MNN
  • Obsolete with no Schneider Electric replacement
  • Suggestions: Try Titan Products or Sontay

DRT3801

  • Room temperature sensor fan switch
  • On/off for CZU, MNN, IAC
  • Obsolete with no Schneider Electric replacement
  • Suggestions: Try Titan Products or Sontay

DRT3851

  • Room temperature sensor fan speed switches
  • As above plus medium and high
  • Obsolete with no Schneider Electric replacement
  • Suggestions: Try Titan Products or Sontay

DU4301

  • Room sensor temperature
  • For MNN & URC
  • New part number: STR601/004604200

DUS4302

  • Room sensor temperature setpoint advanced
  • basic sensor
  • New part number: STR613/004604800

DUSF4351

  • Room sensor temperature setpoint adjustable fan
  • auto/on/off fan override
  • New part number: STR609/004604400

DUSF4352

  • Room sensor temperature setpoint advanced fan
  • Auto/1/2/3 fan override
  • New part number: STR610/004604500

DRTE2201

  • Active room detector
  • Basic sensor
  • Obsolete with no Schneider Electric replacement
  • Suggestions: Try Titan Products or Sontay

DRTE2801

  • Active room detector
  • On/off
  • Obsolete with no Schneider Electric replacement
  • Suggestions: Try Titan Products or Sontay

DRTE2851

  • Active room detector
  • Off/low/medium/high
  • Obsolete with no Schneider Electric replacement
  • Suggestions: Try Titan Products or Sontay

DRH7702

  • 2% 0-10V DC humidity only
  • For KMC, MMC, IAC, MNN
  • New part number: SHR100/006902340

DRH7703

  • 3% 0-10V DC humidity only
  • For KMC, MMC, IAC, MNN
  • New part number: SHR100/006902340

DRTH7712

  • 2% 0-10V DC humidity with Satchwell
  • NTC TEMP OUTPUT For KMC, MMC, IAC, MNN
  • New part number: SHR100-T6/006902420

DRTH7713

  • 3% 0-10V DC humidity with Satchwell NTC temperature output
  • For KMC, MMC, IAC, MNN
  • New part number: SHR100-T6/006902420

DDT

  • DDT1701, DDT1702 and DDT0001
  • Duct sensor non-adjustable
  • New part number: STD660 5126030000

Contact Details:

  • Titan Controls: http://www.titancontrols.net/
  • Sontay Controls https://www.sontay.com
Labels (3)
Labels:
  • Field Devices
  • Satchwell MicroNet
  • Satchwell Sigma
Tags (3)
  • Find more articles tagged with:
  • 5213
  • DavidChild20
  • GaryMontague20
Was this article helpful? Yes No
No ratings
Contributors
  • RandyDavis
    RandyDavis
  • DavidFisher
    DavidFisher
  • DavidChild
    DavidChild
  • Gary
    Gary
  • Product_Support
    Product_Support
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric