Program BACnet B3xx controllers to monitor parent BCX1 Online status

Issue

How to get BACnet B3xx controllers to know whether its parent BCX1 is online with its MSTP network or not.

Product Line

Andover Continuum

Environment

  • BACnet B3xx
  • BCX1
  • MS/TP Network

Cause

There may need to be some action taken if communication is lost with the parent controller.

Resolution

Use the BACnet attribute of System_Status of the BCX1 with BACnet full path in the B3xxx's PE program. Make sure that you need to delay the program with enough waiting time, otherwise, it could make the MSTP congested. For example:

Line Checking
  If BACnetDevices\MyBCX4040 System_Status = Operational then
  Goto Wait10Secs

Line Wait10Secs
  If TS > 10 then
  Goto Checking

Line E
  'Do something to process the BCX offline situation in the b3 controller.
  Goto Wait10Secs
Tags (1)