Issue
How to open an I/A Series G3 station in offline mode.
Product Line
TAC IA Series
Environment
I/A Series G3 WorkBench (all versions)
Cause
There is a need to configure/program an I/A Series G3 station without the station running.
Resolution
- In Workbench, expand My Host:
- Navigate to My File System > Sys Home > stations
- Look for the name of the desired station and expand it
- Find 'config.bog'. Expand this and the station can be configured/programmed offline.
Below is a screenshot showing an example for accessing the demo station offline.
After making changes to the station, make sure to save the changes by right-clicking on 'config.bog' and selecting 'Save'. If this is not done, the changes will not be there the next time the station is run and opened online.