Network 8000 MN-HPFC Issues When Used in EBO

Network 8000 MN-HPFC Issues When Used in EBO

Issue

Digital SAT outputs are not available when using the EBO MN-HPFC object

Product Line

TAC IA Series.

Environment

  • I/A Series Network 8000 MN-HPFC
  • Building Operation Automation Server Premium
  • Building Operation Automation Server

Cause

The standard MN-HPFC device object in EBO cannot be used when the device was previously configured for Satellite Mode used in a Network 8000 system or R2 integration.

Resolution

Use the MN:MicroNet 2000 Generic object to interface to an MN-HPFC when configured for satellite mode.  This object provides a set of generic inputs and outputs that map over to the satellite controller points.  See the attached MN-HPFC Reference Manual that details the inputs and outputs starting on page 6-11.

 
DIN6 ( Digital Input 6 ) controls DO1 Sat Cmd
DIN7 ( Digital Input 7 ) controls DO2 Sat Cmd
DIN8 ( Digital Input 8 ) controls DO3 Sat Cmd