MicroNet 50 series logging module configuration

MicroNet 50 series logging module configuration

Issue

The enhanced logging module in the 50 series does not continue logging once full if not configured to do so.

Product Line

Satchwell MicroNet

Environment

  • MicroNet
  • VisiSat
  • Logging
  • Object
  • Cascade
  • Logs

Cause

The old logging object when the logs were full over wrote the oldest values automatically. The current 50 series logging object requires additional linked for the logging object to function the same way.

Resolution

Updated June 2019
The MicroNet 50 series range MN350, 450, 550, 650 LCD and Touchscreen have been withdrawn from sale.
The IAC 420, 600 and Touchscreen have now also been withdrawn from sale.
No direct replacement is offered.
Further information on these changes can be found in PA-00495 - Notice of Withdrawal - Satchwell Sigma and PA-00528 - End of Commercialization - Satchwell Sigma.

----------------------------------------------------------------------------------------------------------------------------------------------------------

The logging object has been enhanced.
An example of the 100 series and IAC logging object is shown here.

An example of the 50 series logging object is shown here.

The original logging object defaulted to log and overwrite the older values and when configured looked like this.

To achieve the same result with the 50 series type logging object, a couple of the logging object external nodes need configuring. and when configured looked like this.

Further information regarding this object can be found in the VisiSat help file and engineering guide.